Hi - this is driving me nuts and I can’t figure it out so any thoughts welcome.

The hive receiver at the boiler is correctly receiving a signal from the thermostat to turn the heating on - but then… nothing! This definitely isn’t a hive communication issue given (a) the hot water via hives works perfectly; and (b) the receiver light turns on.

It looks as though there are two motorised valves. When the hive hot water turns on, the motorised valve activated and the boiler fires up. But when the hive central heating turns on, the motorised valve does nothing and the boiler doesn’t fire up. I am therefore thinking that the issue is somewhere between the hive receiver and the motorised valve that controls the heating flow. Does that make any sense?

If so, does anyone have any suggestions on how to go about resolving? I’ve checked the wiring - in particular into the hive receiver - and nothing is lose.

Any advice much appreciated!
 
Normally, for both heating and h/w, the thermostat (in your case Hive) switches the motorised valve, and the motorised valve, when completely open, operates an internal microswitch which supplies power (via the orange wire) to the boiler.
The Hive doesn't power the boiler directly, as I guess you already understand.
Sounds like the heating valve may be the problem - either not getting power, jammed, or motor packed up etc.

PS If your valve has a lever to manually operate it, have you tried pushing it fully over to see if the boiler comes on. Only on some valves does the lever go as far as operating the microswitch, so this is not a conclusive test!
 

Reply to Boiler doesn’t want to listen to (Hive) Thermostat in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
277
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
447
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock