I'm looking for advice please for what equipment to use for air pressure testing of copper pipework (for cold & hot water services).

The client is asking for a test of min 7 bar for 24 hours.

Info on 'wet' water pressure testing also useful.

MTIA
 
Air pressure at 7 bar v dangerous, I’d go water every time
 
Would not be doing that with air Jim its very dangerous mate , always use water off the mains and then pressurise it up with a test pump to 7bar , i will sometimes do it to test a carcass but never ever to those sort of pressures. Cheers kop

Screenshot_2018-03-28-05-02-30.png
 
Fill a pipe up with 7 bar of air and the fitting comes off or the pipe fails you could have grit, gravel swarf , solder in the pipe it will be like being shot and the noise when it blows will damage your hearing ,could even blowup in your face use water above a 1bar is my advice . kop
 
Fill a pipe up with 7 bar of air and the fitting comes off or the pipe fails you could have grit, gravel swarf , solder in the pipe it will be like being shot and the noise when it blows will damage your hearing ,could even blowup in your face use water above a 1bar is my advice . kop

But that would be the same as testing at 7 bar with water wouldn't it? Still dangerous
 
But I think what he’s saying is that with sir there’s no protection from debris in the pipes. Water will dampen it down. Plus water cannot be compressed
 
It's the volume with air stores a hell of a lot more energy than water
 
Ive got to pressure test a large Carcass this week, I’ll air test up to 1bar for half hour, to make sure System is complete. Then test with water and a hand pump up to 6 bar (the pressure of the expansion valve PRV) for an hour
 
Ive got to pressure test a large Carcass this week, I’ll air test up to 1bar for half hour, to make sure System is complete. Then test with water and a hand pump up to 6 bar (the pressure of the expansion valve PRV) for an hour

I just fix boilers so all a bit to technical for me.
 
Status
Not open for further replies.

Reply to Air pressure testing equipment in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I've air tested pipework for years, typically 4 bar for 30 minutes. I've never had an issue with any pipework that has passed that test...
Replies
8
Views
497
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
490
losing pressure
L
Looking for any ideas to help. I've a Heatrae Sadia Hot Water tank, heated through Oil fired boiler (working fine). A week ago I reset the air...
Replies
8
Views
322
Hi, I'm looking for a water pump to pump water from a storage tank at a constant 3 bar pressure. It's at a campsite I run that's at the bottom of...
Replies
2
Views
131
Hi all I've finished running the copper for my concealed shower valve and tested both inlets and the outlet with cold mains (full pressure). I...
Replies
1
Views
515
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock