I have to bleed one of the rads every week for 5-6 seconds.
There is a possibility that you are bleeding hydrogen not air.
If you are talking about bleeding off ca 100ml of gas per week I suspect it is more likely to be your new radiators and pipework generating the 'passivating layer', which is a process that liberates a certain amount of hydrogen. Inhibitor slows this process, so it can take several months to complete, but doesn't stop it completely. Another possibility, if the system or pump is noisy, is turbulence due to excessive circulation speeds damaging the passivating layer, which will then liberate hydrogen as it tries to reform.
I would check the pump speed is correct first. Then wait until the system has had several (my system took four) months to settle down. If it's still a problem get the installer to take a sample of the gas and test its composition (i.e. air or hydrogen). Don't do this yourself as most amateur methods are dangerous. (Actually, I've seen installers use methods that IMO are dangerous in the past but they are trained and insured so it's their problem!)
Sentinel sell a System Water Check kit that retails for about ÂŁ50, which involves you taking a sample of water and posting it to a laboratory for analysis. The report will tell you what's causing the evolution of the gas. Most likely cause, IME, is high chloride levels due to flux not being washed out properly by the installer. There are more exotic reasons possible in principle, but I've never heard of anyone having them in a domestic system.
Useful further information here:
How To: Control Corrosion in Central Heating Systems | Sentinel
C.