Hi,

Ive posted this before but still not found the cause of the problem. I have a sealed S plan system with expansion tank that is drawing in air. I have to bleed one of the rads every week for 5-6 seconds. Details below:

1. The system is NOT loosing any pressure until of course I bleed the radiator. I left it alone for 3 weeks and the pressure when cold remained at 1 bar.
2. There is sentinal inhibitor in the system and i have also added sentinal leak sealant.
3. There are NO visible leaks anywhere. I have checked all rad valves and connections.
4. The expansion tank appears to be fine and has 1 bar pressure.
5. No visible leaks on the pump.
6. Worcester Bosch have been out and inspected the boiler and found no issues.

What the Damn is going on?! Have I got a magical heating system that defies the laws of science?

Many thanks

Marc
 
How many radiators do you have? are they small or large? Are they doubles or singles and how much inhibitor did you put in to the system?
 
Its a big house..15 rads with 2 very big doubles rest are singles. Lots of drops too if that helps as downstairs floor is concrete.

I put 1.5 bottles of sentinal in.

Also Ive tried igniting the gas but it didn't ignite so dont think its hydrogen.
 
Sentinel x100 is a good inhibitor but for a system your size I would use 2 x 1 litre bottles. As a 1 litre bottle only does 8-10 rads have you have the condition of the water in the radiators tested?
 
No. I should mention all the rads are new and the system was drained down and refilled 6 months ago. Most of the pipe work is new too. Can you buy testing kits for the water?
 
did you check the expansion vessel pressure when the system pressure was at 1 bar or did you drop the system pressure to check it?
 
i did it when the system was cold.

and the system pressure was at 1 bar cold ?

you normally need to drop the system pressure below the pressure that the expansion vessel is charged to.
 
Where is the pump in relation to the expansion vessel ?
Can you post a photo of the installation of the pump and vessel?

What pipe material is it?
If it is plastic, is it the correct one (barrier) ?
Most of it is these days but you never know !
 
Last Plumber,

Photo attached. All pipework is copper.

Jay,

So the expansion vessel has to be below the pressure of the system??

IMG_20170418_101027447.jpg
 
Status
Not open for further replies.

Reply to Air getting drawn into sealed heating system in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Oil boiler (now~15 years old) unvented system with 17 radiators. We moved in 5 years ago and I had to keep bleeding the same radiator. The bleed...
Replies
1
Views
265
Hi, I am replacing our 11 year old boiler (due to H.Ex. leak) with a new one. This is in a "sealed" system with red expansion vessel in airig...
Replies
3
Views
546
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
506
losing pressure
L
Any ideas why a sealed system with a combi could be grabbing air. The upstairs rads have air in and the system reads 3 bar cold. When the air is...
Replies
28
Views
2K
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
401
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock