If you have a flow temperature of 80 degrees and the rads are all getting hot, then that is the best you are going to get for heat in your property as currently installed and insulated. It us unlikely that there is anything wrong with the boiler.
If you want the boiler to operate more efficiently as a condensing boiler the flow temp needs to be reduced to give a return temp of less than 55 degrees C.
The temperature restriction on the Danfos TP1 can be removed by the parameters on menu 3 or 4 on installer settings