Discuss Hot water from Valliant Boiler in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Margaret,

I find this quite odd. Are you sure that the installer of the boiler was aGas Safe registered individual and that the installer of the system (if different) was a a credible plumber?

The issues you describe and the actions being taken just don’t seem credible to me.

On the basis that the boiler is performing properly, any reputable plumber should be able to diagnose (and probably fix) the problem with your hot water on site within 1 to 2 hours.

A good rule of thumb, is to diagnose the problem, think through the solution then get your tools out and implement it. Be very wary of people get their tools out before having thought through what the problem is
 
Margaret,

I find this quite odd. Are you sure that the installer of the boiler was aGas Safe registered individual and that the installer of the system (if different) was a a credible plumber?

The issues you describe and the actions being taken just don’t seem credible to me.

On the basis that the boiler is performing properly, any reputable plumber should be able to diagnose (and probably fix) the problem with your hot water on site within 1 to 2 hours.

A good rule of thumb, is to diagnose the problem, think through the solution then get your tools out and implement it. Be very wary of people get their tools out before having thought through what the problem is

Hello Brambles, he was obtained from Valiant website to have a valiant boiler installed, he is also on the gas safety register website.

Upon completion, initially, I did had to chase for the paperwork completion to obtain the 10-year guarantee and received this. (1) buildings regulation compliance gas safety certificate letter from vaillant; (2) buildings regulation certificate of compliance issued by vaillant; (3) Vaillant letter that my 10 years extended guaranteed.

I do recall when British Gas (BG) came on 24/04/2019 (was here for 2.5 hours), BG said might need to lift the flooring in the airing cupboard where the blue HW cylinder sits to see the pipe works but told me to contact the installer. I called for the installer and he came on 30/04/2019 checked the Drayton valves and the black airlock switch, having done the purge manually without using hive and lifting hallway floor boards to look for a T pipe or something, he then went to change the pipes in the kitchen from straight 2 straws to criss-cross. He then tried to test for HW and there was air sound splurging sound, he said the HW was still going in reverse flow. At the last resort, he said he still couldn't understand why the HW is reverse flowing that he then said may need to lift the flooring underneath the hot water cylinder tank in air cupboard.

At present, everything is left on running CH + HW, all radiators turned down and waiting for his return.

Hope this clarifies.
Thanks
 
Last edited:
Hi Margaret, I see in your response to @Brambles that the heating SYNCHRON motor was changed, yet the issue could be the hot water one.

Hello CMW1982, yes, I see on my very first OP on this forum that it was the heating synchron changed and the installer said that to me.

To note, he tried testing hot water by removing and not having the drayton cubes attached/connected to CH pipe and HW pipe. I recall that both B.Gas and himself held the HW drayton cube to their ears. Not sure what they listening to.

By the way, why would the CH Drayton synchron need changing if new and less than 6 months?
 
Last edited:
Hello CMW1982, yes, I see on my very first OP on this forum that it was the heating synchron changed and the installer said that to me.

To note, he tried testing hot water by removing and not having the drayton cubes attached/connected to CH pipe and HW pipe. I recall that both B.Gas and himself held the HW drayton cube to their ears. Not sure what they listening to.

By the way, why would the CH Drayton synchron need changing if new and less than 6 months?

I wouldn’t know on that as things fail for a reason be it poor quality or poor system conditions.

Regarding the listening, they may have been trying to hear the motor turning or even the microswitch.
 
Hi Margaret, are you still in the same scenario?

I’ve just been studying your photo of the cylinder cupboard, and I could be wrong (I am tired)but want to clarify something that’s bugging me. Are you able to photograph the yellowed markups on photo more closely? I want to see if the chrome valve is open, and also where that 15mm pipe tees in. I’m trying to figure out I feel your flow and return are piped up wrong. The Magnaclean states flow of water one way, but it could be another way?

58D5AE2C-6750-47E1-B4DF-02CA15A842BA.jpeg
 
Hi Margaret, are you still in the same scenario?

I’ve just been studying your photo of the cylinder cupboard, and I could be wrong (I am tired)but want to clarify something that’s bugging me. Are you able to photograph the yellowed markups on photo more closely? I want to see if the chrome valve is open, and also where that 15mm pipe tees in. I’m trying to figure out I feel your flow and return are piped up wrong. The Magnaclean states flow of water one way, but it could be another way?

View attachment 38466

Morning CBW1982, yes, I am still in the same scenario. Please see photograph markups more closely, (these were how they were situated (24/04/2019). The installer, he visited 30/04/2019 and said he will leave them off and they are not hanging on the pipework at present). Thanks a lot.

00.JPG


01.JPG


02.JPG


03.JPG
 
If I read those photos correctly, the flow is being directed into the DHW tank through both the flow and return connections.

Boiler Flow being directed to the two two port valves (HW and CH) and the magnaclean! HW return connection connected to the Magnaclean on the flow side. Ie. Flow to flow on the HW circuit when the two port valve is opened.

Margaret, I cannot see that this installation has been plumbed in by anyone with basic plumbing or heating engineering experience.

If I include the work undertaken to switch flow and return in one if your earlier posts and your comment that the valve actuators have mbeen left disconnected - it has all the signs of the work being undertaken by someone with a very low level of understanding as to how an S plan system works.

You need a normal plumber to come in and instal the pipework in a conventional manner for an S plan system. Thereafter, to check the connections and commission the Nest controller.
 
Last edited:
Morning Margaret, thanks for the photos. Sorry to be the bearer of bad news, but as @Brambles has said that looks like it’s been done unprofessionally, (but I think you knew that). It is fixable, but not sure how you go about trying to reclaim costs from your original installer, as if it were me I wouldn’t have him back. There is an isolation valve (chrome valve circled in my edited photo) turned off, and flow is either going backwards from magnetic filter (magnaclean) or the flow comes up to a closed off iso valve and through the return. Either way for this to function as it should then it needs sorting.
 
Last edited by a moderator:
If I read those photos correctly, the flow is being directed into the DHW tank through both the flow and return connections.

Boiler Flow being directed to the two two port valves (HW and CH) and the magnaclean! HW return connection connected to the Magnaclean on the flow side. Ie. Flow to flow on the HW circuit when the two port valve is opened.

Margaret, I cannot see that this installation has been plumbed in by anyone with basic plumbing or heating engineering experience.

If I include the work undertaken to switch flow and return in one if your earlier posts and your comment that the valve actuators have mbeen left disconnected - it has all the signs of the work being undertaken by someone with a very low level of understanding as to how an S plan system works.

You need a normal plumber to come in and instal the pipework in a conventional manner for an S plan system. Thereafter, to check the connections and commission the Nest controller.

Hello Brambles, thanks for the above. Just wanted to mention, in case I typed incorrect, I meant that the installer, he said he will leave the Drayton off and not attached to the pipework (it is dangling down and not 'clipped' onto the CH pipework). Hope this clarifies that part.
 

Reply to Hot water from Valliant Boiler in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
My disabled daughter’s hot water has stopped working. It’s a relatively modern Potterton boiler with an indirect sealed hot water system and a...
Replies
12
Views
924
The Water Board have just replaced the main water supply to our property. We have a ground floor combi boiler. The central heating system for the...
Replies
9
Views
546
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new...
Replies
0
Views
283
MartinPod81
M
I live in an apartment with a cold water tank. The cold water tank feeds the cold water tap in the sink and the bath. Recently, I refurbished my...
Replies
2
Views
192
After some advice, i have recently had solar panels fitted and have an Eddi which uses the energy we generate to heat the cylinder using the...
Replies
2
Views
541

Newest Plumbing Threads

Back
Top