Hi. Please can someone help. I'm in the process of a refurb in the house and replacing existing Stelrad horizontal radiators for new Vertical Designer type Radiators. I want to make sure I get the BTU ouput required to heat the rooms. I've done the online BTU calculator and I also have the BTU total outputs for the old radiators, but when looking online it's just a mindfield of T ratings/ Delta T50/T60/T65 etc etc against the BTU outputs indicated and some show the same radiators but give different T ratings against the BTUs eg: 10000 Btu/Tested at T65 and another says it's T50. It's all very confusing and all i want is the correct size radiator with the right amount of BTU output for the rooms. Some sites also mention flow rates and the boiler system I have. I have a New Worcestor Greenstar 40CDi Classic Regular and the system is a Condensing system. Please help !!!! URGENT
 
I use 60 but with the new rulings I've started to use either 40 or 50

Guide below

IMG_3856.PNG
 
Hi. Thanks for that. How do I know what flow and return rate my system is using ? and if the Radiators on the website are showing they are tested at T50, then I'm well covered if mine is T60, but it they are tested at T65 then do I need to convert the BTU/Watss to get a T60 or T50 ? If yes, what is the conversion factors
 
Should say on your boiler / temperature adjustment
 
For a condensing boiler the lower the better but at some point the radiator would be too big. Your existing system would be sized for whatever kind of boiler was originally installed, so simplest to go for a similar output to those. But if you're replacing them all then go for lower.
My experience is our system we have replaced most of the radiators with D40 but that means that when running the boiler at the right temperature for the new rooms the old rooms don't really warm up properly. If we turned the boiler up we would have to limit the flow through the new rads to get a much bigger temp difference across them.
 
Delta T can have more than one meaning. If you talk to a boiler engineer it is the difference between flow and return temperatures. So a flow of 75C and return of 65C gives a DT of 20C. But to a radiator man it is the difference between mean rad temperature and room temperature - as explained by ShaunCorbs.

Modern condensing boilers are designed to work with a (boiler) Delta T of 20C. Condensing does not occur unless the return temperature is below 55C. So the flow temperature should be no more than 75C (55C + 20C). This gives a mean water temperature of 65C. Assuming a room temperature of 20C the rad-room delta T is 45C. So you should use this when selecting your radiators. You could use a delta T of 40C with flow = 70C and return = 50C, but this will mean the radiators will be about 20% larger.

You say that you have calculated the rads required for each room and that you need a 40kW boiler. This seems very large - particularly if you are refurbishing a house and, presumably, upgrading the insulation etc. How have you arrived at the boiler size and which online rad calculator did you use?
 
Hi. I already have a 40kW boiler reason is I am only refurbing the downstairs and replacing the radiators there eg: new kitchen and a knock through. No extension, but this is a big house, 3 storey and m2 for the whole downstairs is approx 125m2 with majority height in rooms of 2.6m with 2 rooms the ceiling being 4.5m !! so not small. Indication: the old radiators in the kitchen had BTU output of 11500 BTU, one room with the 4.5m ceiling averaged around 9500 BTU so working on 40C isn't an option i would freeze and the water would be cold. I used Stelrads BTU Caluculator
 
Sorry the 11500 BTU figure was spread over 3 Radiators in the Kitchen/Breakfast area. this warmed the area fine. Also new Aluminium Double Glazed windows going in, previously they were wood double glazed. House is 16 years old of Brick and Block construction... use all this info in the BTU calculator.
 
The old boiler was either 30kW or 35kW. So who recommended a 40kW?

As you are only doing partial refurb., that changes things. The rads in the rest of the house will have been sized assuming a rad Delta T of 50C. (75C flow, 65C return, 20C room) If you now run them with 75C flow and 55C return their output will be reduced by 15%. You may get away with it as rads tend to be oversized.

Make sure the installer knows that you have sized the rads assuming a 20C differential at the boiler, with 75C flow and 55C return.


The Stelrad calculator is very good - provided you put in the correct information. :(
 
Seems to be quite a bit of misunderstanding here.

The OP has a regular boiler which has to heat a Megaflo indirect cylinder so this must set the flow temperature any lower than 70 deg C and the domestic hot water temperature of 60 - 65 deg C will not be achieved. (Unless Weather comp is being used giving the boiler the ability to run heating at lower temps). The boiler is designed to run trying to achieve a 20 deg C drop so it is looking for a return water temp of 50 deg C which is just low enough to allow a little bit of condensing with starts at 53deg C.

If rads are used as the heat emitters then the room temperatures are recommended to be 21 deg C for all rooms except bath / shower rooms which should be 22 deg C (D.H.D Guide & B.S en). As previously stated, we take the designed room temp from the Mean Water Temp in the rads (70+50/2 = 60MWT - 21room temp = 39) so the Dt for selecting rads is 39.
Most rad manufacturers provide tables of outputs based on BS en 442 which requires them to be running with a Dt of 50 therefore if you don't do some sort of correction the selected rad would not provide the stated output leading to cold rooms when the outside temp gets to the designed level (normally -1 or -3 depending on whereabouts you are in the country).
 
Radiator manufacturer often base their output figure on on Top & Bottom Same or Opposite End pipe connections which increase the output against piping the the common English way of Bottom Opposite Ends so again a correction should be provided. 39 = 0.724 x 0.96 for BOEs = a correction factor of 0.695
 
The boiler sounds like it is oversized & it is highly likely that the original rads were selected based on the old design of 82 - 71 MWT - 76.5 - room temps and may well be older than the double glazing or other insulation all of which has changed the heatloss I would strongly suggest doing a heatloss calculation for each room to which a new rad is required that way you will know the required output once the correction factor has been applied. (& the boiler output requirement can be confirmed & not guessed at).
 
Many folks are being conned , well not conned more mis directed as many companies are selling there rads with the delta t of 60 which is fine if you want 10 degrees room temp but since the ruling was changed to delta t 50 there's still too many companies still using dt 60 ! But yeh they should be made to use btu output @ dt40
 
Seems to be quite a bit of misunderstanding here.

The OP has a regular boiler which has to heat a Megaflo indirect cylinder so this must set the flow temperature any lower than 70 deg C and the domestic hot water temperature of 60 - 65 deg C will not be achieved. (Unless Weather comp is being used giving the boiler the ability to run heating at lower temps). The boiler is designed to run trying to achieve a 20 deg C drop so it is looking for a return water temp of 50 deg C which is just low enough to allow a little bit of condensing with starts at 53deg C.

If rads are used as the heat emitters then the room temperatures are recommended to be 21 deg C for all rooms except bath / shower rooms which should be 22 deg C (D.H.D Guide & B.S en). As previously stated, we take the designed room temp from the Mean Water Temp in the rads (70+50/2 = 60MWT - 21room temp = 39) so the Dt for selecting rads is 39.
Most rad manufacturers provide tables of outputs based on BS en 442 which requires them to be running with a Dt of 50 therefore if you don't do some sort of correction the selected rad would not provide the stated output leading to cold rooms when the outside temp gets to the designed level (normally -1 or -3 depending on whereabouts you are in the country).
The boiler control-stat setting does not necessarily affect condensation in CH mode. I have a heat-only boiler with Honeywell system W (either/or diverter valve). The control-stat is set at about 70°C and when HW is calling the boiler goes off and on several times before the cylinder stat is satisfied. But in CH mode, except in exceptionally cold weather, it doesn't get near control-stat setting before switching off on the room-stat, so the actual setting makes no difference. It plumes and produces plenty of condensate.
I'm not keen on mid-position valves as with that I believe when both stats are calling the HW cylinder would be cooled, and have to catch up when the room-stat's satisfied.
To ensure condensation, need plenty of rad area which can dissipate the boiler output at low DT as you say. But then the control-stat setting doesn't affect it. Outdoor temperature compensation could make things better still, but would need to be either/or for CH and HW, with the compensation ignored and going to full control-stat setting in HW mode.
 
Many folks are being conned , well not conned more mis directed as many companies are selling there rads with the delta t of 60 which is fine if you want 10 degrees room temp but since the ruling was changed to delta t 50 there's still too many companies still using dt 60 ! But yeh they should be made to use btu output @ dt40
Quite right Kris the introduction of BS en 442 was supposed to provide a level playing field by making them all use Dt 50.
 
That's my point if everyone stated their products in T50 or delta 50 which is supposed to be the current set standard you know exactly where you are. But they don't and it has just complicated it all. I just want to know what radiators to get
 
The boiler control-stat setting does not necessarily affect condensation in CH mode. I have a heat-only boiler with Honeywell system W (either/or diverter valve). The control-stat is set at about 70°C and when HW is calling the boiler goes off and on several times before the cylinder stat is satisfied.
What is your cylinder fixitflav ? is it by chance an older copper indirect. Do you know the the kW rating is of it's coil?

You are correct with a modern cylinder on at the same time as the heating it is unlikely to be adequately fed by the boiler but I prefer to just use the programer to bring the hot water on 40 - 60mins before the heating comes on, in that way achieve the same result i.e. hot water heats in the required time as per Building Reg's & full boiler power is available when the heating is required.

so the actual setting makes no difference. It plumes and produces plenty of condensate.
Not sure I understand what you are getting at - The boiler is not in condensing mode if it is producing lots of pluming ?
 
That's my point if everyone stated their products in T50 or delta 50 which is supposed to be the current set standard you know exactly where you are. But they don't and it has just complicated it all. I just want to know what radiators to get
You can use the following to find - F1 =
( actual Dt degC ) 1.3
catalogue Dt deg C
F1 is the correction factor
A scientific calculator or spreedsheet will be required.
 
Last edited:
What is your cylinder fixitflav ? is it by chance an older copper indirect. Do you know the the kW rating is of its coil?
It's a copper indirect, foam insulated, about 20 years old. I don't know the kW rating. Whatever it was when new it will be a lot less now, I would guess not more than about 3kW. It takes about 30mins to recover, but I don't find that a problem. If it was I could turn the control-stat up higher.
I dread to think how much scale there is on the coil. I've changed 2 cylinders, this one 20 years ago, and one 20-odd years before that. In both cases there was close to a bucketful of scale.
I prefer to just use the programer to bring the hot water on 40 - 60mins before the heating comes on
I suppose that's an option, I just leave my HW on 24/7. It only calls about once/day.
Not sure I understand what you are getting at - The boiler is not in condensing mode if it is producing lots of pluming ?
That's a good point, I had tended to assume the plume was a sign it's condensing, but it could be a bad sign. It depends on where condensation to visible vapour occurs. If it's after it leaves the boiler the latent heat is lost, but if it's inside, the latent heat could still go into the circuit water, but the condensed water going out with the plume rather than into the condensate trap.
 
It's a copper indirect, foam insulated, about 20 years old. I don't know the kW rating. Whatever it was when new it will be a lot less now, I would guess not more than about 3kW. It takes about 30mins to recover, but I don't find that a problem. If it was I could turn the control-stat up higher.
I dread to think how much scale there is on the coil. I've changed 2 cylinders, this one 20 years ago, and one 20-odd years before that. In both cases there was close to a bucketful of scale.
A new cylinder (Part L complaint) would likely have a coil rated around 18 - 21 kW's, depending on its size, all designed to give a recovery time of 20mins (given that the boiler power is available) in that way the return water temperature is low so the boiler does not cycle on/off on the boiler stat & it should be in condensing mode longer.
 
That's my point if everyone stated their products in T50 or delta 50 which is supposed to be the current set standard you know exactly where you are. But they don't and it has just complicated it all. I just want to know what radiators to get
Why not just get rads, based on the current set standard T50, to give your calculated output in each case? If your boiler flow and return are 75° and 65° that will give your 50° DT. Giving some condensation, but in practice most of the year the actual flow temperature will be well below the control-stat setting 75°, so you'll get more condensation, as I was saying in #16. In any case your selected rads are likely to be the next standard size up from your calculated output, which also helps.
then do I need to convert the BTU/Watts to get a T60 or T50 ? If yes, what is the conversion factors
Conversion is 10000BTU/h = 2.93kW. (To be pedantic, BTU is energy, not power, but everybody understands the implicit per hour, so there's rarely any confusion)
 

Reply to What Delta/T Rating should I be working on for Replacement Radiators in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
198
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
240
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
354
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
253
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock