Following a full refurbishment of an house and a new build rear extension we had a brand new heating system installed. Give you an idea of what it is:

  • Vaillant 637 system boiler
  • 300l Water tank
  • Wet UFH (floor area 15x4m) in new rear extension (family area, kitchen and dining) - used all day (1 zone). Unknown but calculated by SOLFEX from what I recall seeing by the heating engineer at the time.
  • Existing Downstairs, existing upstairs each with own zone (2 zones).
  • 5 bedrooms (1 guest so hardly used), 3 bathrooms.
  • 17 Aluminium radiators in total 25Kw in output excluding UFH (i don't the KW what this actually is)
  • Honeywell Evohome with Y87 wall stats in each zone
1 year in and our gas bill seem very high, much more than anticipated. Approx. 45,000Kw used.

I've been many forums over the past week or so and it does seem that my usage is much higher than standard (18Kw-20Kw).

The past week I've also been monitoring evohome and I can see that the UFH once up to heat even in this cold weather spell (-1 degree) it maintains a lovely 19 degrees all through the day with just the odd call every couple of hours for a bit of heat (10% or so) and switches back down to 17 through the night (i can see that it does'nt drop lower than 17.5 through the night using some logging software so no heat demand).

The downstairs zone (non UFH - 9 radiators - approx 14KW - downstairs includes bedroom 5 and ensuite) seems to be running most of the day to maintain a temp of 19.5 degrees. I've witness it "cycling" every 10 minutes or so throughout the day.

This morning, i've changed the D00 setting to 24KW, previously it was set to 37KW and see if that makes any difference.


I also took the following readings if it helps:
Flow temperature is: 75C
Return temperature is: 65C

Should I just wait and monitor our smart meter over the next couple days and see if it as any impact??

I've noticed that the max reading on smart meter shows is 22.84Kw since I've made the change to D00, however it goes down only as low to 6.8Kw.

Any other advice??? Is this to be expected??? Oversized boiler???

Thanks in advance.






 
Hi,

Smart Meter readings for month of Jan as follows: 1st jan: 4220 and 31st 4936. 716m3 of gas...converted to KW: 8074.

My energy supplier is Tonik and Positively Green v20 tarif. 2.9p/Kw and 22.37p standard charge.
 
Hi,

Smart Meter readings for month of Jan as follows: 1st jan: 4220 and 31st 4936. 716m3 of gas...converted to KW: 8074.

My energy supplier is Tonik and Positively Green v20 tarif. 2.9p/Kw and 22.37p standard charge.
how many people , and a building lifestyle is handy.
ie how many carpet rats ..wrinklies ..etc like me. ..
do you all leave the building
5 days a week or run a home office...see what I mean ?
centralheatking
 
Three adult and 2 young children.
Occupied downstairs throughout the day. However, from 10-4pm we turn down the standard downstairs heating (radiators) to 19degrees. The extension area is where we spend most of the day (kitchen,dining room and family room) and this is heated by the wet UFH at constant 19.5degress from 6am to 8pm which takes an 2.5 hours in the morning to get the desired temp but then maintains it easily throughout the day into the evening with only a couple of times for gentle heat call.
 
Three adult and 2 young children.
Occupied downstairs throughout the day. However, from 10-4pm we turn down the standard downstairs heating (radiators) to 19degrees. The extension area is where we spend most of the day (kitchen,dining room and family room) and this is heated by the wet UFH at constant 19.5degress from 6am to 8pm which takes an 2.5 hours in the morning to get the desired temp but then maintains it easily throughout the day into the evening with only a couple of times for gentle heat call.
ok ...wow ...so ur system is never off essentially . later We will go over it ..you must be loaded ..but hey
centralheatking
 
So you technically have the heating on alday every day???

25kw known for rads
KW for ufh needs to be known
KW for 300l invented cylinder (5kw...others can correct me)

So without knowing the output of the ufh. You still need 30kw output on the boiler unless the timings for hot water to come on where different schedules to heating

By rating the output on the boiler to 24kw I think you said it's just not going to heat the house effectively.
 
Sounds about right if your in the house all day
 
Smart Meter readings for month of Jan as follows: 1st jan: 4220 and 31st 4936. 716m3 of gas...converted to KW: 8074.

That's roughly twice the volume of gas that I would have guessed based on your description the house and usage patterns. I'm assuming you're in England not the North Pole, of course.

The two areas I'd scrutinise carefully are:

Firstly, the UFH, in particular what's the specification for the construction of the floor? If there isn't enough insulation under it, or there is two much insulation on top of it, UFH can be a really money-pit.

Secondly, the hot water. How much do you use per day and how is it programmed? Have you got a hot water leak somewhere?

Unless your house is essentially uninisulated or you leave all the windows open the whole time, the amount of gas you are using if it were all dissipated as heating would be baking you all alive. This is why I'm suspcious about the hot water. You might be pouring money down the drain, literally.

There is always the possibility that the meter is faulty and is over-reading. Also, are you sure that your meter is not also supplying a neighbour?

Once you done some basic checks, I suggest you get a heating engineer to do an energy consumption and loss calculation for your house to see how much it should be costing you. They'll also be able to check, approximately, that the consumption rate indicated by the meter matches the rate expected when the boiler is working.

I'm probably repeating stuff others have already because I got interrupted for several hours while typing this answer.
 
Let's just assume your newly refurbished house is reasonably well insulated and your UFH meets the latests building regs.
Your boiler still won't be able to provide the necessary flow rates at delta T20 to your system without a low loss header or other means of hydraulic seperation, that's why I suspect your boiler flow temps are so high (inefficient) and as a consequence you're burning more gas than you should be.
 
That's roughly twice the volume of gas that I would have guessed based on your description the house and usage patterns. I'm assuming you're in England not the North Pole, of course.

The two areas I'd scrutinise carefully are:

Firstly, the UFH, in particular what's the specification for the construction of the floor? If there isn't enough insulation under it, or there is two much insulation on top of it, UFH can be a really money-pit.

Secondly, the hot water. How much do you use per day and how is it programmed? Have you got a hot water leak somewhere?

Unless your house is essentially uninisulated or you leave all the windows open the whole time, the amount of gas you are using if it were all dissipated as heating would be baking you all alive. This is why I'm suspcious about the hot water. You might be pouring money down the drain, literally.

There is always the possibility that the meter is faulty and is over-reading. Also, are you sure that your meter is not also supplying a neighbour?

Once you done some basic checks, I suggest you get a heating engineer to do an energy consumption and loss calculation for your house to see how much it should be costing you. They'll also be able to check, approximately, that the consumption rate indicated by the meter matches the rate expected when the boiler is working.

I'm probably repeating stuff others have already because I got interrupted for several hours while typing this answer.

The UFH is set in a 65mm liquid screed, under which is the celotex insulation all to regs and done professionally and then porceline tiles on top. The UFH in this cold weather does take around 2.5 hours in the morning to get to temp, but what I notice is that it rarely comes on throughout the day (monitoring the heat call from evohome) and back on for a top up 30 minutes in the evening.

The hot water is puzzling me to be honest, it was set since we had the system installed (2 years ago) to come on every morning at between 5-6am. But I have turned this off the timer around a week to see if this had any impact. We still have lots of hot water (no one complained that water gone cold). What I have observed is that occasionally the hot water pipe leading from the valve to the tank is hot so this telling me that the boiler is at times automatically reheating??? or is this the tank automatically asking for the water to be heated as its dropped below a certain temperature?
 
Last edited:
The hot water is puzzling me to be honest, it was set since we had the system installed (2 years ago) to come on every morning at between 5-6am. But I have turned this off the timer around a week to see if this had any impact. We still have lots of hot water (no one complained that water gone cold). What I have observed is that occasionally the hot water pipe leading from the valve to the tank is hot so this telling me that the boiler is at times automatically reheating??? or is this the tank automatically asking for the water to be heated as its dropped below a certain temperature?

You need to look into this and get it sorted. If, for example, the HW zone valve is jammed open you could have a 'hydronic short circuit', which would explain the small differential temperature between flow and return, which will lower the efficiency of the boiler significantly.
 
Have you a secondary hot water circuit?

Just checked this morning, there is a dedicated secondary hot water circuit to feed the 5th bedroom/ensuite (furthest away from boiler). Not sure if the mechanical timer was actually in "timer" or "off" mode as it was half way between. Anyway, it was 8.5 hours behind current time (so showing 12:30am at the point I checked this morning). I've ensured its in the off mode and also moved all the little timer sliders to off position so at least I know its for sure not going to come on now. So i'm now wondering if the hot water circuit was coming on early hours of the morning and also again mid afternoon circulating hot water around and actually causing the water tank to cool down? Its during these periods I've noticed that the temp in HW tank drops and then the boiler seems to turn on itself.

I've been monitoring the gas smart meter reading after the heating turns off for the night and again before it turns on in the morning (I know painful). I've noticed consistently that there is at least 10KW used overnight and according to the smart meter the call for gas around 1am and then again at 5am. Once again around mid afternoon of 5KW, all when there is no demand from heating (i.e. target temp is lot lower than current temp).

Lets see what happens today and overnight and I will feed back. Good spot by the way!!!!

So one of my previous question was, if the boiler temperature does drop will the boiler automatically reheat it???? if so whats driving this??? is it the thermostat on the hot water tank?
 
Secondary hot water circuits are energy thief’s, as the pump is circulating the hot water, it’s cooling the cylinder down...as water in the loop is continuously losing heat, the situation would be worse if you had little or no lagging on the pipework.
 
Last edited by a moderator:
Okay, so I noticed the boiler come back on this afternoon again even though there is no heat demand or timer requirement for HW. So checking the flow pipes to each zone, only the hot water flow was hot which feeds the HW tank. I looked at the boiler stat attached to the tank and it was on 65 (max). I turned it down a bit to say 45 and I could hear the hot water value make a noise (closing??) and then followed by the boiler turning off. It never came back on since...I've turned the stat back to approx. 55C.

So it seems, that regardless of timer settings for HW (which by the way I turned off beginning of Feb to see impact of hot water supply) we have never been without hot water as the boiler keeps it to temp. I wonder if this could also be the reason it coming on middle of the night to reheat the water due to temperature drop?
 
So it seems, that regardless of timer settings for HW (which by the way I turned off beginning of Feb to see impact of hot water supply) we have never been without hot water as the boiler keeps it to temp. I wonder if this could also be the reason it coming on middle of the night to reheat the water due to temperature drop?
If you turned the HW off at the timer but the cylinder is still being heated, I would say there is definitely something wrong with the way it has been wired up.

What sort of insulation does the HW cylinder have - none, loose red jacket or fixed insulation? Modern cylinder with fixed insulation will keep hot for many hours. Our one stops heating about midnight and the water is still hot enough for a shower at 10am the next day.

60C is the recommended temperature as it kills of any legionella bacteria.
 
If you turned the HW off at the timer but the cylinder is still being heated, I would say there is definitely something wrong with the way it has been wired up.

What sort of insulation does the HW cylinder have - none, loose red jacket or fixed insulation? Modern cylinder with fixed insulation will keep hot for many hours. Our one stops heating about midnight and the water is still hot enough for a shower at 10am the next day.

60C is the recommended temperature as it kills of any legionella bacteria.

Hi,

Its a valliant Unistore 300l unit.
 
I turned down the thermostat on the HW tank (experiment) down to 40 degrees before I went to bed. Checking the smart meter before the heating came this morning there was no gas usage :). Also observed the hot water tank temperature at 43"

So can conclude that the HW is on permanent regardless of timer settings to maintain the temperature of the HW tank. The heating will turn off after 10:30am, i'll then turn up the HW thermostat back to 60 degrees and expect it to turn back on. I'll report back....thanks once again for everyone expertise help.
 
Fork and Knife. 45000 kw hr a year! That’s a lot.

Have you just moved in? Or have you heating bills from this house or previous ones?

If it’s a complete refurb ... is it an old house? What age? Does it have solid brick walls. Did the refurb include insulation.

If you post a pic of the brickwork we can see if it’s solid or cavity walls.

My daughter had a leak in her hot water system. 2 litres a minute. So the boiler was constantly heating hot water that was leaking away under the floor. I reckon this cost her £80 a month. 3000 kwhr a month ... 36000 a year. Her boiler was constantly switching off and on.

Have you a water meter? Look at that ... see how much you use overnight. Or turn off the main water supply. The heating will still work fine, the boiler will heat up, you won’t get hot water. but can’t heat any more cold water as it’s not getting to the cylinder.

Did you say you had a smart meter? Is Gas being used all the time?

We only have our water heated once a day, for one hour. Cylinder is well insulated and it keeps hot for a long time ... we shower so don’t use that much water.

Has the bill always been that high?
 
Last edited:

Reply to High gas bill - Vaillant 637 - UFH and Alu Rads - Help in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
187
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
228
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
257
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
232
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...