i did a check on this boiler and i got a reading of .0009 and a co2 % of 10.3%, i looked in mi and it asked for a % of 9.8 but it did not give any parameters is there a method to work this out ,or does anyone know for this model is it acceptable
 
I think max is 9.8% plus or minus 0.5. So 10.3% is on the limit so I would adjust down if doing a service. Min is 9.2% plus or minus 0.5% I believe.
 
woresters can be very tempermental,had a fault of intermitant hot water,checked everything worcester tech said,did fga,just slightly out
altered to mi,hot issue sorted,was a learning curve that one
 
Yes thats right 9.8% max in service mode +/- 0.5% so 10.3% max what are ppm co when testing should be below 200 and 0.002 co/co2 % not 0.004
 
i did a check on this boiler and i got a reading of .0009 and a co2 % of 10.3%, i looked in mi and it asked for a % of 9.8 but it did not give any parameters is there a method to work this out ,or does anyone know for this model is it acceptable
Did you let heat for at least 10 mins before your FGA?
In any case 10.3% is on the limit so would be your choice wither you want to start messing about with it to bring more into line. Personally I avoid messing around with gas/air ratio valves as much as possible and would leave it at that.
 
Status
Not open for further replies.

Reply to worcester junior 24 i flue gas analyser results in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to...
Replies
9
Views
351
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
564
  • Article
A Plumber Who Worked Illegally Gets A Suspended Sentence After Falsely Claiming To Be Gas Safe Registered. A Plumber in Herefordshire was...
Replies
0
Views
260
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the...
Replies
5
Views
336
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
478
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock