So, i think its all right,
I have my browns to the blue, and red,
Which run back up to the out puts from cylinder stat and room stat..
 

Attachments

  • 16790840840038688585199588665829.jpg
    16790840840038688585199588665829.jpg
    413 KB · Views: 12
So turn the heating on prog should give you 240 to the room stat

Turn the room stat up you should have 240v on the 2 port brown and the 2 port lever should go slack

Correct ?
 
So turn the heating on prog should give you 240 to the room stat

Turn the room stat up you should have 240v on the 2 port brown and the 2 port lever should go slack

Correct ?
Il check after my scampi and chips🤣
Just now, i called for hw, time i got to boiler, pump was running, boiler screen was live, but not lit up, boiler wasnt firing, cover off valve, lever had moved and pressing switch, pulled supply to brown, pump stopped, lever released, boiler screen shut down...
 
NB the colours of the cables except from the zone valves could be misleading to say the very least.

I recommend you confirm all the connections

does your boiler need PL and SL ?
 
NB the colours of the cables except from the zone valves could be misleading to say the very least.

I recommend you confirm all the connections

does your boiler need PL and SL ?

Yes 330 does need both
 
Im not sure tbh. What happened. I took front off boiler, messed with the sensors on flow and return, i took the cover off the board, removed it, contact spray and cleaned all connectors, found a couple of small areas of corrosion, reassembled.
Re bled rads, bled the air valve on the hw coil return.
It fired on hw demand.

Going to let it run and warm for a bit. Then try the hot water side of things...
May not be home and dry yet, but its progress.
Again many thanks for all your help.
 

Reply to Wiring s plan from old set up y plan...? in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Customer complains of Intermittent heating on Y plan with Stat satisfied. New boiler fitted last year (no permanent live required or fitted...
Replies
25
Views
2K
Hello. I've just replaced our old Potterton EP2 CH controller with a Drayton Wiser HubR (& peripherals). The old backing plate wasn't...
Replies
1
Views
302
Hi All, Looking for a bit of advice on the best way to pipe this. - 24kW Worcester regular boiler in kitchen, approx. 9 years old - unvented...
Replies
16
Views
1K
have moved a pump by new boiler so could wire for pump overrun as no live in airing cupboard, but now I am worried about air ingress into the...
Replies
3
Views
758
Hi I seek some advice on replacing an existing regular boiler. I currently have an old Potterton 10-16 Netaheat electronic, which is around 35...
Replies
7
Views
698
Back
Top