Discuss Why does my perssure keep going up? in the Central Heating Forum area at PlumbersForums.net

Messages
4
Any idea why the pressure keeps going up on my combi boiler? I have a Vaillant Ectotec Plus about 15 years old. The heating has been off all summer and the filling loop taps are both fully closed but the pressure keeps going up. I empty about 2-3 litres of water from the system every 2-3 weeks. It's been like it for about 3 months.
The only thing I can put it down to is taht both filling loop taps and leaking water into the system but it seems unlikely for both taps to develop faults at the same time. As far as I understand, that's the only way pressure is going to get into the system. Am I missing something?

Any ideas?
 
Does this go up after use, or does it go up without use? It could be the filling loop, easiest way to diagnose that one is to disconnect the loop. There could also be a pinhole in the plate heat exchanger, easy one for that is to isolate the cold main going into the boiler underneath, you‘ll have no hot water whilst this test is carried out.
 
Last edited by a moderator:
Does this go up after use, or does it go up without use? It could be the filling loop, easiest way to diagnose that one is to disconnect the loop. There could also be a pinhole in the plate heat exchanger, easy one for that is to isolate the cold main going into the boiler underneath, you,k have no hot water whilst this test is carried out.
Thanks for the advice. It's when it's not in use. I haven't used the heating since April and this started about June/July. I'll take on board the advice and come back if I need more help. Thank you.
 
You might consider doing this first thing tomorrow morning while the system is cold, shut off the cold feed to the combi, at the boiler, if possible, if not, at the main isolation valve, open a hot tap to depressurize the plate heat exchanger, and leave open, check boiler pressure and if greater than 1.5bar, reduce it to 1.0 bar, fire up the boiler with all rads on, observe the boiler pressure when system up to full temperature, if the pressure is > say 2.7/2.8bar, then more than likely E.vessel problem.
 

Reply to Why does my perssure keep going up? in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi All This is following on from thread I made a few days ago but can't seem to find I'm in a bit of a bind with my CH design where I want to...
Replies
0
Views
441
Got up on Wednesday morning no hot water, (only cold water coming out of hot tap). Checked boiler, it had zero pressure and F1 fault showing. So I...
Replies
16
Views
1K
Hi, I need to drain my vokera 29 boiler in the attic as Im going away for 4 weeks at least to make sure there are no frozen pipes. In my small...
Replies
1
Views
305
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
478
W
  • Question
My Worcester Combi Boiler is not working, instead the display flashes on and off repeatedly, as shown in <a href=" View...
Replies
1
Views
444
Back
Top