Hi

I have a Vokera 15 vhe boiler and all has been running well for the last 6 months since moving in up until a few weeks a go.

Boiler throws up a flashing 79 code.
Try restarting the boiler straight away but I have to wait 10 minutes for it to cool down before it works.

I reset the boiler after 10 mins and all works well until the end of the next day when the heating switches off and the boiler temperature climbs to around 90 on the display and then throws up this code again.

Have to wait for it to cool down before resetting.

My boiler was set at a temperature of 70c but after having this problem I turned it down to 65c but still the same problem.

Turned it down to 60c same problem

Turned it down to 55c Same problem

Turned it down to 53c works fine and have done for a couple of weeks.

Turned it back up to 60c problem starts again.

Problem is having it on 53c seems to take forever to heat the house up to a reasonable temperature.

I can put it on 70c but don't want to reset the boiler every night once the heating turns off.

Any suggestions before I call a professional.

Not looking to fix myself but rather have a better understanding before getting ripped off for something it's not.
 
That boiler may be a heat only boiler with a external circ pump, this might be installed in your hot press or close to the boiler, you may also have a mid position 3 port valve or a number of two port (motorised) zone valves, if you have the mid position valve, no need for the ABV, if a number of two port valves, the ABV, if installed, will be close to and between the pump and these two port valves.

Below, you have a ABV, a two port valve & a three port mid position valve.

s-l1600.jpg


5106oLYGH9L._AC_SL1000_.jpg


1706131111634.png
 
The pump is running at max setting, CC3 which is > 6M so the setting on the ABV, 0.4?, 4M, should be quite adequate to to allow the ABV to open when the boiler/burner trips on shutting the HW and CH zone valves, the pump then, if wired correctly should run on (overrun) for ~ 3 minutes to cool down the boiler heat exchanger.

Can you feel the pipes on either side of the ABV with boiler running, are both sides hot?, then switch off CH & HW and see if the pump runs on for a few minutes and check if (ABV) pipes are now hot (if not previously).

How many rads have you got?.
 
The pump is running at max setting, CC3 which is > 6M so the setting on the ABV, 0.4?, 4M, should be quite adequate to to allow the ABV to open when the boiler/burner trips on shutting the HW and CH zone valves, the pump then, if wired correctly should run on (overrun) for ~ 3 minutes to cool down the boiler heat exchanger.

Can you feel the pipes on either side of the ABV with boiler running, are both sides hot?, then switch off CH & HW and see if the pump runs on for a few minutes and check if (ABV) pipes are now hot (if not previously).

How many rads have you got?.
14 rads.

I will run a test tomorrow when the boiler is on for the heating in the evening. I will come back with my findings.

Thanks for your help.
 
You can check the pump overrun any time (maybe first) just start the boiler on either HW or CH, then shut it down after a few minutes and see if pump runs on for a few minutes, if not, that should be addressed.
 
You can check the pump overrun any time (maybe first) just start the boiler on either HW or CH, then shut it down after a few minutes and see if pump runs on for a few minutes, if not, that should be addressed.
Hi,

Heating has been on for 2hrs.
Rooms have hit temperature and the heating has now switched off.

Both pipes either side of the ABV are hot
Pump cut straight off with heating.
 
Pump is probably wired incorrectly Matt, it should be wired directly from the boiler which should supply the overrun period, it's probably wired fom the zone valves auxiliary contacts that tell the boiler to fire when any one zone valve is open.
 
Pump is probably wired incorrectly Matt, it should be wired directly from the boiler which should supply the overrun period, it's probably wired fom the zone valves auxiliary contacts that tell the boiler to fire when any one zone valve is open.
Ok thanks for your help.
Big/costly job to put right or easy fix?
 
Probably a few hours work but check first that your boiler has the overrun.
Hi Mate,

So I'm having a bit of trouble getting somone to do this job.
I have tried getting a couple of quotes over the weekend but none seems interested in actually running the cable.
The boiler is downstairs in the kitchen and the pump is up stairs in the bathroom. (Opposite ends of the house) probably not worth their time.

I have measured up and I'm looking at around 20m of cable.

I might have a go at running the cable myself and then getting a sparky in to connect up.

What size cable should I be buying?
1mm 3 core good enough?
Would it need to be heat resistant cable or anything special?

Thanks
 
I have measured up and I'm looking at around 20m of cable.
Assuming permanent live mains is available where the pump is, there is a 'radio' link option that could avoid the hassle of having to run a cable. Here's an example - it costs about £100, so you might prefer hard wiring!

 
Assuming permanent live mains is available where the pump is, there is a 'radio' link option that could avoid the hassle of having to run a cable. Here's an example - it costs about £100, so you might prefer hard wiring!

Thanks for posting this.

looks like a much better solution.
👍
 
It sounds like your Vokera boiler is overheating when set above 53°C, leading to the error code. This could be due to a faulty thermostat, circulation issues, or a blockage in the system causing restricted flow. Before calling a professional, check if the radiators are evenly heating and if there's any noise indicating a pump or flow problem. Understanding these symptoms can help diagnose the issue more accurately and prevent unnecessary repairs.
 
It sounds like your Vokera boiler is overheating when set above 53°C, leading to the error code. This could be due to a faulty thermostat, circulation issues, or a blockage in the system causing restricted flow. Before calling a professional, check if the radiators are evenly heating and if there's any noise indicating a pump or flow problem. Understanding these symptoms can help diagnose the issue more accurately and prevent unnecessary repairs.
This response doesn't make any sense, as the issue has been identified and resolved. Are you a Bot?

Edit: Seems likely since "Activate Trade Training" use website developers, who are, to quote:

Combining Creative Marketing with Cutting-Edge AI

 
Last edited:

Reply to Vokera 15 vhe Boiler in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
127
I have a green star ten yrs old keeps increasing pressure, feel on off filling valve not working, drain off to recommended, but after few days it's increased whilst cold...is this a regular problem.
Replies
1
Views
140
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
447
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock