But u haven’t got just a normal combi u got a combi that as u say is giving u restricted 14l then you got the xtra storage supply from internal cyl adding xtra litres
And this is what your not getting
The only thing I need to check out is d36 giving u the o/p of combi only and not both ?
I think valliant were trying to say that the tank is always the feeder for the heat exchanger. So it’s not extra capacity being added in after the incoming cold water is added, it just means the water goes back through and requires a little heat.
This seems to imply that the cold water will be diluting in the tank all the time so the burner would have to ramp up as time passes on, eventually getting to a point where the storage tank is only cold.
I didn’t think it worked like this, however would explain my issue to some extent. This also means the tank wouldn’t be “recharging” where there is a constant drain as that’d not be possible. It would have to wait until demand has gone then recharge.
Any other views?
[automerge]1592642444[/automerge]
How do I put it in to status mode? I haven’t seen an option for this. Cheets
[automerge]1592644481[/automerge]
But u haven’t got just a normal combi u got a combi that as u say is giving u restricted 14l then you got the xtra storage supply from internal cyl adding xtra litres
And this is what your not getting
The only thing I need to check out is d36 giving u the o/p of combi only and not both ?
[automerge]1592641332[/automerge]
Put boiler into c mode check your status reading should be s21 to s28 c mode
If it’s s10 to s17 normal dhw mode
If not changing to S21 to s28 boiler faulty
Found it
Comfort mode off sequence = S.31 > S.21 > S.23 > S.24 >S.20 > S.27
Comfort mode on sequence = S.31 > S.21 > S.23 > S.24 > S.27
So it appears to S.20 labelled "DHW Demand" that isn't present on comfort mode off.