Brilliant explanation Chris. No offence meant by the college tutors thing. Mine were brilliant and were very much up to speed, sorry the op seemed to imply his weren’t quite so
Absolutely no offence taken Riley!! :cool:
I know all about the poor levels of knowledge & experience out there in FE land. When you have seen store man or newly qualified Plumbers stuck in front of a class & asked to deliver this very technical subject it is no wonder there are so many poor people out there.
It was just to point out (& as you found) there are still a few of us who try very hard to stay on the cutting edge, mind you what is all this malarkey about controlling a boiler via your hand held telephone....? :p
 
Just done quick pipesize calc and for 8 metres gas pipe, 8 bends and 1 tee on 60kw nett boilers smallest gas pipesize is 35mm. On your picture you show 28mm but then 15mm + couple of bends to boiler . Pressure drop through this would be huge. For these size boilers should be 35mm to as close to gas inlet as possible then 35mm to 22mm reducer then 22mm to 1/2 conex to boiler.
You need gas safe engineer to work out properly. You mention original gas pressure were 16mb. Not sure whether this is at meter or appliance but too low and no gas safe engineer would commission at these pressures as appliance would be classed as “at risk”.
Looking at picture it looks like a diy install, cables all over place.
Best to get Vaillant out to do properly.
 
16mb is not too low and i would commission a boiler at this pressure. All boilers sold in the UK have to work properly at pressures down to 14mb. The only thing you have to maintain is the 1mb drop accross the installation pipe work. And yes his gas pipes are probably undersized but we dont know where his metre is in relation to the boilers so we can't know for sure. he's also getting the same issue when only one boiler is working, in which case the 28mm supply would be adequate.
 
Last edited by a moderator:
The only thing you have to maintain is the 1mb drop accross the installation pipe work..

How would you achieve or confirm that 1 mbar drop?

Would you add a test point at the end of pipework just before the boiler isolation valve?

Sorry as i had not seen any engineer install a test point in there, apart from commercial (for tightness testing mainly)

As most of posts in many forums will say the P1 at the gas valve is the test point although gas safe Register Technical Bulletins (tec bulletin 129 published 16 February 2016) acknowledges a possible drop of 0.5-2.5 mbar at the inlet side of the appliance gas control valve.

The Gas supplier must provide a minimum of 19 mbar at the outlet of EcV at peak flow conditions. The pressure drop across primary meter can be up to 4 mbar, leave us with 15 mbar take drop of 1 mbar for pipework then its 14 mbar, and average of 1.5 mbar drop through the appliance pipework and then you end up with a reading of 12.5 mbar at Inlet to boiler gas valve.

I think, and please do correct me if am wrong on this: the key issue in this whether the pressure drop affects the safe operation of the appliance or contibutes to a fault condition then GIUSP should be followed and a Gas rate will confirm a satisfactory operation (GSIUR 26.9(c)) Esp with the zero govenor or Air/gas ratio valves where burner pressure measurement is not appropriate
 
The maths will tell you if your pipework to appliance is below 1mbar drop. What the appliance will work at is inconsequential as this prerequisite must be met in the first instance.
 
Could this scenario some how cause the boiler has supply issue as it’s just ignites and then switches off due to the demand not being required anymore?

I’m mechanically competent and used to restore classic cars. If you start a car but switch it off without it fully turning over it sometimes results in it flooding and difficult to start the next time. In very layman terms could this happen with gas?

How are you getting on, anything to update?
 
New posts

Reply to Vaillant boiler issues F28 on ecotec 430 not the normal culprit in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I am looking for a heating engineer to diagnose and resolve an issue with my Vaillant EcoTec 832 combi boiler. Job Location: Copeland Rd...
Replies
1
Views
424
I recently had a new 2023 Vaillant ecoTec plus 630 (30kW) system boiler installed along with a Low Loss Header (LLH) in my house. I have 21 rads...
Replies
10
Views
805
H
I need some help and advice with a boiler issue. We have F29 and then F29 appearing on our new boiler. This happened after few days where water...
Replies
1
Views
254
Hello everyone, I'm facing an issue with my Vaillant EcoTec 832 boiler and would greatly appreciate your expert advice. The Problem: Heating...
Replies
8
Views
978
Hi all Wondering if you could help with this strange issue. I have a Vaillant ecotec 637 (set to 20kw part load) which was connected via a LLH...
Replies
57
Views
3K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock