Just a quick question. I've been asked to fit a Worcester Greenstore unvented cylinder but I'm worried flow rate is insufficient. I measured the flow rate at 14 L/PM. It currently comes into the house in 20mm mdpe and goes straight to 15 mm after the stopcock to supply the house.
I would fitting new 22mm mains pipework to supply the cylinder. What effect would this have on the flow rate/pressure?
It's a whole house refurb so all new pipework and new boiler/cylinder. They currently have a traditional set up in place.
Hi guys.
I measured the flow rate at 14 L/PM. It currently comes into the house in 20mm mdpe and goes straight to 15 mm after the stopcock to supply the house.
I've just read the Greenstore installation instruction and I've extracted the following: In a domestic installation, 1.5bar working pressure and approximately 15/20 litres/min. should be regarded as the minimum. Consideration should be given to upgrading existing 1⁄2" (15mm) cold mains pipework to a larger size, if the recommended minimum working pressure/flow rate is not being achieved. Maximum pressure is 5.5bar. Therefore I would recommend increasing the internal pipe size (Stopcock to UVDHWC) to 22mm.
From reading the post it does appear as though you have very little experience of G3 installations so my advice would be to either take your time and read the MI completely, or get yourself on a refresher course for G3 - it'll only cost you around £150 for a day and you'll have the knowledge you need to feel confident with this kind of install.
Status
Not open for further replies.
Reply to Unvented cylinder flow rate requirements? in the Plumbing Jobs | The Job-board area at PlumbersForums.net
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.