ok, so I have a underfloor heating manifold with 11 ports (see pic)

Rooms struggle to warm up. Think I know why, here's what I've tested:
1. Pressure expansion tank in garage 2 bar - ok
2. Boiler working, water hot - ok
3. Thermostats calling for heat and actuators respond - ok
4. Flow: all meters were totally corroded, had to bin and put new ones (see pic)
5. New flow meters show minimal flow (0.5 - 1 lt pm)
6. Checked valves, opened all fully, no stuck pins - no change to flow
7. Flushed system with garden hose, line by line, no air locks

So, it seemed flow was the problem. To test this I closed the return valve and all actuators, and opened the drain valve on the pipe directly from the pump (I.e. flow side)This showed me the pump was delivering 7lt pm, and the water was piping hot (steam off the bucket).

To check the rate the water was going through the underfloor heating pipes, I closed the drain valve on the flow side, and opened one actuator and opened the drain valve on the return side, and closed the return valve, so water would only flow through the underfloor pipe and then through the drain. This showed 7lts pm was flowing through, so same as the flow side, I.e. No blockage.

THE ANSWER?
Is the problem just that the system is only getting 7lts pm? I'm thinking that at an average of 1.5 lts pm, per port/line, it might need a total input flow rate from the pump of around 15-20 lts per minute? If this is correct, is the pump the problem?

PUMPS
there's a pump directly on the manifold (standard Grundfos - see picture), and there's a pump in the garage (looks higher tech - see pic), and not sure how these may support each other?

I'm wondering if the corrosion on the flow meters might suggest other components could be corroded and not working properly. The pump sound normal. I have unscrewed the valve and no air in it.

CAN YOU DIAGNOSE THE PROBLEM??

Mike
 
Not enough flow.

Either mixing valve, pump or both.
If the flow meters were as bad as that, I would change the mixing valve. Undo the screw on the pump and see if you can stop the spindle with screwdriver, by pushing gently - if so, replace pump capacitor ( if available ) or replace pump
 
The image isn’t the clearest, but are those two 15mm coming down to feed the manifold or been tee’d into the 22mm circs and go off and feed a radiator?
 
image.jpg
image.jpg



The image isn’t the clearest, but are those two 15mm coming down to feed the manifold or been tee’d into the 22mm circs and go off and feed a radiator?

Yes, this manifold is on the first floor. We have a loft room above, which we wanted a radiator in, so teed off for this, I think the plumber used two thumb valves that were sitting there ie took these away and used for the 15mm pipe connection. You can see where - it's the two 'u' bend 15mm pipes, scorch mark behind the left one. Currently this radiator and controller are both off, so don't think it is causing the problem by, say, drawing flow, but open to guidance.

I have attached better pictures of that bit.

And here's a really dumb question: how do I get the biocide inhibitor into the system??

Mike
 

Reply to Underfloor heating, I've done the donkey work testing, can you diagnose in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to...
Replies
6
Views
289
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
464
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16...
Replies
0
Views
240
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock