Hi John.g
Thank you for your message.
Here are the parameters:
d.001 5 minutes
d.002 20 minutes
d.014 speed target AUTO
They look like the default settings.
d.002 setting of 20 minutes results in a actual anti cycle time of 6 minutes based on a your boiler target temperature of 60C (look up table).
The pump auto setting looking at the boiler/pump characteristic seem to indicate that the minimum flowrate is 500LPH or 8.3LPM at 7kw output which means a deltaT of 12C and ~ 1300LPH or 22LPM at 38kw giving a deltaT of 25C. This will obviously only apply to a UFH (or rad) system that is directly fed from the boiler or where the boiler flow temp and the UFH mixed flow temp are equal which they arn't.
You say that the boiler deltaT is only 10C, by my calcs it should be ~ 19C and give a very economical return temp of 41C (bags of condensing) and if it actually is 10c then the boiler internal (or external)by pass, or is operating, but a boiler return of 50C still is quite OK.
The reason that the boiler isn't able to get away on the first refiring after a anti cycle time of 6 minutes may be because the boiler flow rate is too low initially but will then increase as the ufh temperatures fall causing the boiler & ufh flows to increase.
Changing the pump mode to setting 3 or 4 may help but at the expense of a lower deltaT.