Hello everyone, I'm a Plumber/ pump man from the Philippines. I need advice regarding pump problem. I dont know if this the right forum, but here it is. Two pumps connected in parallel runs continuously. What puzzled me is that whenever I partially closed main discharge valve or any of the discharge valve of both pump the pressure drops. Now this my first encounter with such a pump. Please refer to attached files. Is it perhaps a variable speed/ discharge pump that reacts to the pressure transmitter installed at the discharge. Pump is servicing a four story building. pressure is 70 psi drops to 50 to 60 whenever I partially close any discharge valve. Looking forward to your advice.
 

Attachments

  • Photo0081.jpg
    Photo0081.jpg
    52.3 KB · Views: 57
  • Photo0078.jpg
    Photo0078.jpg
    69.6 KB · Views: 50
  • Photo0067.jpg
    Photo0067.jpg
    38.2 KB · Views: 46
  • H pump.png
    H pump.png
    16 KB · Views: 49
  • H pump.png
    H pump.png
    16 KB · Views: 38
  • Photo0078.jpg
    Photo0078.jpg
    69.6 KB · Views: 42
Grundfos CR10`s 12m head multi-stage booster pumps there. One speed non variable 3kw motors @ 3500rpm and no pressure transmitter on them. Don`t understand why you would want to throttle back the discharge or are you getting cavitation.
I'm just testing if the pump can still deliver more pressure. There is a pressure transmitter installed next to the pressure gauge.
 
Is that the boosted cold
[automerge]1573417565[/automerge]
Does it feed a tank onntop of the four storys?
[automerge]1573417832[/automerge]
Its trying to maintain a constant pressure.
When you close it do you only lose pressure on one side
 
Last edited:
What is this pressure transmitter, can you post photos of it please?
[automerge]1573419680[/automerge]
I'm just testing if the pump can still deliver more pressure. There is a pressure transmitter installed next to the pressure gauge.
Is that the boosted cold
[automerge]1573417565[/automerge]
Does it feed a tank onntop of the four storys?
Looks like it is in a workshop at the moment.
 
Last edited:
Is that the boosted cold
[automerge]1573417565[/automerge]
Does it feed a tank onntop of the four storys?
[automerge]1573417832[/automerge]
Its trying to maintain a constant pressure.
When you close it do you only lose pressure on one side
Yes it is boosted cold
No it does not feed a tank on the top floor it has a pressure tank next to it.
Its connected in parallel so both lose pressure. Yes I think its trying to maintain a constant pressure
[automerge]1573426079[/automerge]
What is this pressure transmitter, can you post photos of it please?
[automerge]1573419680[/automerge]


Looks like it is in a workshop at the moment.
The transmitter has a wire that runs to the control board. That is why I was thinking that maybe " the control board sends command to the motor based on the transmitter reading" That is why I was thinking the motor is variable speed. I dont see an auto bypass valve either.
[automerge]1573426281[/automerge]
there is only one pressure gauge on the discharge side of both pumps that sits next to the pressure transmitter.
[automerge]1573426507[/automerge]
The pressure transmitter is connected to the pressure gauge with a tee and has wire that goes to the control board
[automerge]1573426676[/automerge]
I think the reason it runs continuously is because its trying to maintain a constant pressure that does not go up to the set cut out pressure.
[automerge]1573428677[/automerge]
I am sorry I think I had said something wrong. Please refer to the layout drawing I made as I try to explain. Actually the discharge valve1 is currently 20% or so open so like 80% close. Whenever I try to open it pressure drops. When I close main discharge valve pressure also drops. So yes I think its trying to maintain a constant pressure. But if it does, why does the pressure dont recover. I have watch there for like 2 min and the pressure never recover. How long does a pressure of such a system recovers? Whenever I close main valve or open valve1 pressure drops within a minute.
 

Attachments

  • Photo0083.jpg
    Photo0083.jpg
    50.4 KB · Views: 36
  • Photo0082.jpg
    Photo0082.jpg
    38.6 KB · Views: 33
Last edited:
It won`t recover pressure, are you getting flow & pressure mixed up. A quick look at Grundfos site say`s outlet should be DN40 which I don`t think you`re showing in the photographs. You won`t get more out than the manufacture states by adjusting inlet/ outlet valves, if anything you will kill it.
 
Looks to me the the pressure transducer notices pressure drop and kicks selected pump in. When its satisfied turns them off.
If there no non returns with the head off water it pass back through pump 1 when you open valve 1.
Also whats the min and max pressure settings set at?
[automerge]1573483070[/automerge]
The pressure tank next to it that you mentioned,
Should think this is more likely the cold feed for the pump to make sure it has volume behind it .
[automerge]1573483140[/automerge]
Agree with rpm these are on off pump sets.
 
Last edited:
Looks to me the the pressure transducer notices pressure drop and kicks selected pump in. When its satisfied turns them off.
If there no non returns with the head off water it pass back through pump 1 when you open valve 1.
Also whats the min and max pressure settings set at?
[automerge]1573483070[/automerge]
The pressure tank next to it that you mentioned,
Should think this is more likely the cold feed for the pump to make sure it has volume behind it .
[automerge]1573483140[/automerge]
Agree with rpm these are on off pump sets.
two pumps run continuously 24/7. But you're right there is no non returns on the head off. I think you're correct with the pressure tank because its just a small one. Not the size to service an entire building. that solves one of my concerns. Excuse my ignorance but what is an "on off pump set"
 
Excuse my ignorance but what is an "on off pump set"

When the pressure drops below the cut in set point the pump(s) switch ON and run at their maximum speed.
When the pressure in the system reaches the cut off set point, the pump(s) switch OFF.

Modern pump systems are variable speed, so the pump(s) reduce speed to keep the pressure constant.

Have you checked that there is no air trapped in the pumps?
 
Quite a lot of variables with this one and it could be a situation where you start with the basics and go on from there.

1/ non-return valves on outlets of pumps
2/ pressure switches - faulty, not calibrated, not connected.
They are there, but not switching off the pumps - obviously not working as intended.
3/ Pressure vessel - shouldn't have much to do with the operation of the pumps or pressure switches on the pumps. It's only there to stop a lag in water pressure when the pumps are stopped and the pressure switch hasn't activated ( very basic description of what it does )
 
Unless I`m looking at this all wrong I would expect to see two pressure gauges on the discharge pipes or one on the pipe after they merge together if they do this.
Also wondering if a photo of the control board might help.
 