Discuss Thermostatic valves dont adjust the temp in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Messages
4
the majority of my radiators have thermostatic valves. Some of these work fine but some of them dont let you adjust the temp.

ie. Setting one or setting 5 makes no difference - the radiator is blazing hot. For small bedrooms this is pain cos the room just heats up too much.

we first discovered this in the smallest bedroom so I got a plumber to replace the valve, assuming that this was the problem. However, not change you can have off or hot but nothing in between.

Am I missing something, but isnt the whole point of them that you can adjust the temperature?! Any ideas about whats going wrong? (or are the valves just a con?!)
 
Mine work quite well, used EPH for the last few replacements, ensure the actuator is fully anticlockwise, max index, before attaching it, normally via a knurled nut that you hand tighten clockwise.
What make are yours.
 

Attachments

  • TRV EPH.jpg
    TRV EPH.jpg
    310.6 KB · Views: 9
Last edited:
They don’t work like you seem to think.

The thermostatic valve senses the room temperature and when this has reached the desired temperature the valve shuts the radiator off.

Whilst the valve is open the radiator will get hot, according to the flow temperature setting on the boiler.

Turning the trv to a lower number doesn’t change the maximum temperature of the radiator, it just affects how long it will be hot for.
 
They don’t work like you seem to think.

The thermostatic valve senses the room temperature and when this has reached the desired temperature the valve shuts the radiator off.

Whilst the valve is open the radiator will get hot, according to the flow temperature setting on the boiler.

Turning the trv to a lower number doesn’t change the maximum temperature of the radiator, it just affects how long it will be hot for.
I think what the OP is saying is that the the TRV is, effectively remaing open, no matter what the setting, whatever ones views on how they operate, they should control the room temperature based roughly on the index settings, above.
 
Yes. I turn the rad on and it gets hot and stays hotm Even if you set it to 1, it doesn't cool down. It's in a small room which gets hot quickly so from what you're saying, it should get hot then the valve should shut off and the rad should cool down until the room temp drops.

It's not doing the shut off and cool down bit!
 
What make is the faulty one?.

If you remove the actuator after first turning it to max, push the valve pin in, it should move ~ 3 to 5mm and spring back out.
 
Last edited:
Will have to take a look when I get home
Hi again. Sorry for delay, have bee away from home.

The valve is from Pegler. It's now not even turning off when set to zero.

Sorry, I don't know the right names for stuff. I removed the plastic top (unscrewed collar beneath it and pulled it off). I can't see a pin, there is a hexagonak nut but the middle of it is just smooth / filled in. (I'm sure when I tried this with the old one there was a pin I tried tapping)
 
It does depend on the heads used, Mothers old house I used Energenie heads, and these show target and current TRV_report.jpg so if the current exceeded the target I closed the lock shield valve a tad until current did not exceed target, and with her modulating gas boiler the rooms were spot on, but this house has oil so the boiler does not modulate so looking at the TRV report I get Report full day.jpg which shows how the room has done throughout the day, this is a Kasa head, the cheap (I paid £15 each in 2019) only shows what set to, not current temperature.

With mothers house when she died the new owners did not what electronic heads, so swapped back to mechanical, now the lock shield valves set, the old heads set at around 2.5 worked great, each electronic head has pros and cons, I find the Kasa (TP-Link) very good Tapo-TRV8.jpg but it is not linked to any wall thermostat, I found a Tuya at £3.90 each, not a clue how good, the Kasa seems to have jumped in price at £55 I paid around £23 at the price now may as well get Hive or Wiser.
 

Reply to Thermostatic valves dont adjust the temp in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi, I need to remove some radiators for redecorating and went to try and shut off the valves either side of my rad. I have TRV on one side and on...
Replies
3
Views
283
Hi I’m new here and don’t know a thing about plumbing so be gentle on me as I am also going to ask a possible dumb question, this summer I turned...
Replies
1
Views
501
I have a heating system comprised of skirting radiators that form part of a loop from the boiler, round the house and back. Some rooms get...
Replies
1
Views
150
Hi all, Our flat has communal heating and our thermostat is set so low so the heating should never be coming on. However over the last 10...
Replies
2
Views
551
Hi, I just moved into a new house and it has a Glow Worm Compact 24c combi boiler and a ESI ESRTP4RF+ programmable room thermostat and I am...