A simple question, but so far I've not found a definitive answer:-
Some older boilers use a thermostatically controlled pump overrun switch built into the boiler thermostat.
They are generally factory set and not adjustable.
At what temperature should it switch?
I'm specifically referring to the Glowworm Fuelsaver MK2 boiler with a Ranco C77p0102 thermostat, but I imagine they are all set to operate at a similar temperature.
I suspect it should be 65degC.
Can anyone confirm this?
Not familiar with the boiler in question, but are familiar with what you are asking.
I have seen boiler stat pump run on settings as low as 40 C, but most I encounter are 50C.
I doubt yours would be 65 C. I would assume 50 C or lower
I think the one in question is currently switching at around 65degC.
The boiler thermostat is several years old so there is a good chance that the pump overrun set point has drifted over time and is now higher than it should be.
The result is that if the boiler thermostat is set fairly low (e.g. '2' on the '1' to '5' scale), then the water temp in the heat exchanger can remain below the pump overrun threshold. When the room stat turns off the boiler, the pump turns off at the same time (i.e. no initial pump overrun). The water temp in the heat exchanger continues to rise for a while and after a few seconds the pump switches back on. It only remains on for about 25 seconds and then is switched off by the pump overrun thermostat. When this happens there is sometimes a disturbing thump noise in the vent pipe as a pocket of water vapour is expelled up into the F&E tank.
If the boiler temperature is increased slightly (e.g. setting '3'), then the problem goes away because the water temperature in the heat exchanger is above the pump overrun threshold and so the pump remains on for longer when the room stat cuts off the boiler.
The pump overrun threshold is factory set and is not intended to be modified: The adjustment screw has thread lock to stop it moving. The problem is that the thermostat is obsolete and I cannot buy a replacement.
Using an old thermostat, I have found that a soldering iron applied to the adjustment screw softens the thread lock and allows it to turn. I think I need to remove the thermostat from the boiler, place the phial in a heated pan of water and use a thermometer to adjust the screw so that it switches at a lower temperature.
Hence my original question about the correct temperature setting for the pump overrun.
You would have thought this information would be published by Ranco but I've been unable to find any documentation online.
If its set and operating normally as you suggest at 65C and the boiler SP is on 60C then you might expect a delay between the room stat switching off the boiler and the pump starting on overrun until the Hx rises to 65C, it should then run on until the stat hysteresis switches it off?
Yes I agree.
I can't really explain the 'thump' noise in the vent pipe unless the pump is sticking when it's switched back on by the overrun stat and the pump is hot. It's hard to pin it down because it doesn't happen very often. I'm sure the pump doesn't stick when the system first starts up and it's cool.
The only difference that I can see is that when running with a low boiler temperature, the pump switches off for a few seconds before being switched back on by the overrun stat. Even when that happens, it doesn't always make a bang in the vent.
Also you say the thump occurs when the pump stops which means the the temperature is or should be "normal" but strange that no thump when boiler SP increased to ensure pump overrun without delay until presumably the temp again falls to the same "normal".
I have seen thumping being caused by excessive pump pressure combined with a mid position valve but one would think that this should occur during normal heating operations as well and the diverter valve should be closed anyway during pump overrun.
You might look at the ABV setting (if fitted)
I can't be sure if the thump happens when the pump starts or stops. It happens infrequently and I've been unable to force it to happen while I'm monitoring the pump. All I know is that it happens shortly after the room stat turns the boiler off.
I did wonder if the 3 port valve could be affecting things. I think the HW cylinder would already have reached its required temperature so the valve would be in the 'heating only' position (port B open, port A closed) at the point when the room stat switches off.
My understanding is that the valve would then move back to its default position with port B closed, port A open i.e. 'HW only'. I'm pretty sure the diverter valve can never close off both ports at the same time. The valve movement would take a few seconds. I'm not sure what effect it would have when the pump starts up while the valve is moving between the two positions? I would not have expected it to give a problem.
I don't think the valve is sticking - I've removed the cover and watched the gears and spindle moving.
It's an old Grundfos pump with three (manual) speed settings.
I usually have it set to the lowest speed where it runs the quietest.
This is the setting where I've heard the thump.
I've also tried it on the middle speed. I haven't heard the thump on this setting, but because the problem is intermittent I can't really be sure if pump speed is a factor.
One would think that lowest speed should be best, also if you have both CH & HW on, the valve is in mid position (A+B) then with no demand for HW the valve will motor towards the heating only (A) position and if then no demand for heating (or HW) will remain with the heating port A open but boiler off so I don't think the valve will be changing over during pump overrun under these conditions.
I managed to find a brand new replacement thermostat.
It was advertised as being for a Ravenheat boiler rather than a Glowworm Fuelsaver MK2 but it's actually the exact same Ranco C77p0102.
When it arrived, I checked the calibration using pan of water and an accurate thermometer.
The results are with the temperature control set to the highest setting (=5).
The boiler switches off @ 77 degC.
The pump overrun switches at 70 degC.
I was surprised that the pump overrun temp is so high.
Now I'm wondering if the calibration is within spec.
I still have been unable to find any documents that specify the correct factory settings.
It would (will) be interesting when you test the old one and see its switching point, based on your new one its probably around 70C so if you are running with a boiler SP of anything below ~ 65C C then probably a pump overrun start delay with this one as well?
It’s possible the thermostat you have bought has a higher sp of 70 when fitted to a ravenheat; but a lower factory setting intended for your boiler?
Ideally I suppose one wants the pump to kick in immediately when the boiler shuts down so the stat should be set at, or slightly lower than the minimum boiler set point which on a condensing boiler may be ~ 40C but on non condensing boilers is around 60C so this stat, even though still apparently calibrated high at 70C may be specifically designed for a non condensing boiler.
A further development...
This evening I discovered that if I turn the room stat right down, the boiler keeps running and the radiators still get hot. I believe the room stat is working. I can hear it click when I turn it.
The only explanation I can come up with is that the 3 port valve is not operating correctly. The HW cylinder gets hot, so could the valve be stuck in the mid position?
While I was trying to diagnose the pump overrun problem I took the cover off the 3 port valve to check it. I thought it was working as I could hear the motor run and I could see the gear wheels turning. Is it possible that the rubber ball may have disintegrated over time?
If the valve is not working correctly that may explain the 'thump' noise in the pipes I sometimes get when the room stat turns off.
The valve is a Honeywell V4073A1039.
See:-
Honeywell motorised valve faults - Free Heating Advice - https://www.freeheatingadvice.com/articles/honeywell-motorised-valve-faults/#Honeywell_3-port_mid-position_valve_operation_V4073A1039_and_V4073A1088
For valves made before 1985, you have to drain the water before you can remove the power head. I think the one I have falls into that category. Just my luck!
You can't replace the entire valve without first draining the HW cylinder, disconnecting it and shifting it sideways to allow the pipes to pull out of the compression fittings. I'm hoping it may be possible to just replace the power head.
Can anyone confirm that it's possible to change just the head without having to remove the entire valve?
does the head (the part that removes to get at the insides eg synchron motor) has a dimple ?
There is no dimple so I'm pretty sure the head cannot be removed without draining the CH system.
I suspect the shaft may be jamming and/or the ball is not seating properly, so the valve body almost certainly needs replacing.
If you look at the earlier photo of the inside of the valve, it would appear that you can remove four screws and replace the top plate, valve ball and drive shaft from a new unit without having to disconnect and replace the main body. Obviously the large O-ring would need to be swapped over from the new unit. Has anyone tried to do this?
As already explained, in my situation there is little free movement available in the pipework. Hence replacing the entire valve would involve draining, disconnecting and shifting the HW cylinder to allow the pipes to be removed from the valve compression fittings. That would involve a lot more work (See the photo below).
Yea no dimple so 4 screws so not removable sorry to say
you should be able to remove that
loosen all joints
undo the back pipe, push the pipe out of the 3 port spin the body so it’s out of the way
undo left and right nuts
push left pipe out of the valve and at the same time remove from cylinder
if you can don’t remove the cylinder connection
I've ordered a replacement valve.
In the mean time I re-checked the operation of the suspect valve.
The shaft definitely turns and it returns to the end stop under the force from the springs when no power is applied. In that position, hot water from the boiler should feed the HW cylinder only.
I've tried setting the programmer to HW only but the rads still get hot.
It suggests the problem may be the rubber ball inside the valve. Has anyone taken an old one apart? Does the rubber harden and no longer provide a seal? Does the rubber disintegrate?
Sometimes they fall off or yes they wear and can let water pass
The HW cylinder bypass gate valve is cracked open about 1/2 turn.
If the valve is open too far, is it possible for hot water to flow through the bypass valve and through the rads in the opposite direction to the normal flow? i.e could the problem be due to 'Reverse Circulation'?
If that's the case then it could it be that the 3 port valve may not be faulty after all.
I need to prove this before I go to the trouble of replacing the 3 port valve.
Reply to Thermostatic pump overrun temperature? in the Central Heating Forum area at PlumbersForums.net
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Hi they used to say as a last resort you could discharge the D2 pipework at high level and turn it back to the wall. Similar to a combi boiler. I...
Can anyone recommend a decent multi meter, preferably under a 100 pounds. It's for checking boiler components so I don't need a top spec one...