I've got a job to replace a Thermostatic Mixer, under a basin in a public premise. When the unit is turned on(service valves) you can hear mains water bypassing to the hot water side, I assume a check valve had broken inside.

Then a though occurred to me do the hw & cw supplies have to be balanced pressure? because the Hw side is fed from a cylinder with a head of about 0.8 bar and the cw is mains.

Thanks
 
Some can work up to 5-1 pressure difference. But best on eaqual pressures.
Non return on the valve can’t be shutting.
 
and also they dont work on gravity pressure (you can Sod faster or it doesnt get hot)
 
Status
Not open for further replies.

Reply to Thermostatic Mixer bypassing in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I live in an apartment block where generally hot water is supplied from the communal hot water cylinder and cold water to bathrooms is supplied from cold water tanks in the loft. It is a vented system. However, in a basement flat and a ground floor flat cold water supply to bathrooms is...
Replies
4
Views
594
V
Hi All, Hope all are doing great. I have replaced two separate tap of my bathtub by mixer tap with thermostat. Previous with two separate tabs, water pressure was strong, but after replacing it by mixer tab with thermostat, the water pressure has lost drastically (in tab as well as shower...
Replies
2
Views
616
Deleted member 120897
D
Hi Guy's, Looking for some advice on an issue I have having with a recently installed thermostatic mixer shower in my ensuite. Everything was working fine for a coupe of months however now the valve has started misbehaving which is resulting in having to turn the temperature valve round further...
Replies
2
Views
395
Hi All Just looking for some advice on which Exposed Thermostatic Mixer Shower (Bar Shower) would go well with the Shower Pump i'm getting installed. So the pump is the - SALAMANDER PUMPS CT FORCE 30 SU REGENERATIVE SINGLE SHOWER PUMP 3.0BAR from ScrewFix - seems like a decent one for the...
Replies
4
Views
609
Looking for any ideas to help. I've a Heatrae Sadia Hot Water tank, heated through Oil fired boiler (working fine). A week ago I reset the air gap as I was having dripping from the pressure relief valve. Since then I've lost a lot of pressure from the hot water feed to my shower. The rest of...
Replies
8
Views
276
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock