Post number of loops, length of each loop, the flow/return flow of each loop, the manifold flow/return temps or any info you have, for example if you have 9 loops with a flowrate of 2.0LPM/loop and with manifold flow/return temps of 45C/37C, dT of 8C then the UFH requires 9X2x60X8/860, = 10.04kw say 10kw and the boiler output will be exactly the same, I thought we looked at this previously?I had the UF heating only come on last night for an hour. It consumed the full power that the boiler is rated up to currently (approx 20kw) for the hour that it came on.
Can anyone help suggest what is the best back of the envelope way to calculate what the UF circuit usage should in theory be? I have an idea of the metres of pipework and pipe centres + floor area overall. Thanks!