A

AaronC

So I got called to a burner where they had the problem of it won't fire in the morning and they have to hit the button on the control box for it to fire. I have changed the pump and the box, but its still doing the same thing? I have checked the oil filter and its spotless, also I serviced it a few months ago and checked the nozzle and its still as good as new. The oil supply is fine too

Anyone any idea what else it could be?
 
Could be a few things. First of all, I assume, as you changed oil pump then the solenoid is new, so it could be motor capacitor or photocell. Also burner could be set wrong which won't start on cold start in morning. Check spark is healthy & that motor seems strong, with no bearing noise.
 
Yep, new solenoid with pump. When we did fire it, there was no bearing noise, sounded healthy enough. In what way would the burner be set wrong that it won't start on a cold morning?
 
It could be overaired, you have to make an allowance for summer settings and winter settings, warm air has less oxygen content than cold air hence if it is a cold morning and the boiler is setup right on the borderline it could have too much oxygen.
I agree with best on everything else, it could also be air in the oil line, check there are no weeping joints. My bet would probably be with the capacitor as Best says
 
Last edited by a moderator:
As Kimbo says, too much air to the oil mixture will prevent it igniting or burning correctly on start up, & can lock out. Very common when we get cold mornings. Usually caused by air setting too high, but obviously if oil pump pressure is too low or nozzle partly blocked, same happens.
Capacitors seem to be a common fault on Sterlings. Try listening carefully to burner motor start by switching burner on a lot of times. If it sounds sluggish on the split second start any one time, then change the capacitor.
 
Last edited:
Sorry, I had said solenoid in last post but meant change capacitor! Have edited it now.
 
Try an ebi transformer had bother with few of these intermedent
 
If the motor turns OK and it only trips when it comes on in the morning, sounds like you are getting air in the fuel line.

Without seeing it, if I were guessing I would suspect the following scenario - fuel supply is lower than the boiler and there is a slight leak in the supply pipework allowing air in, causing the oil to fall back down the pipe to its natural level due to gravity. The air coming in is only gradual so it's only when the boiler has not been operating for a significant length of time that the oil has run far enough back down the supply pipe that the fuel does not reach the pump before the controller times out.

Rectification - firstly the usual culprit for this is a wheel head fire valve as these are prone to leaking as they age. Use a Rothenberger type pressure test pump on the line (at the tank end) and when you pressure it up with oil (6 bar), the leak will become obvious.
 
Last edited:
Status
Not open for further replies.

Reply to Sterling Burner Problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
221
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
117
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
106
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
316
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
181
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock