Discuss Sime ecomfort. No hot water unless heating is on in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

MK Heating

Gas Engineer
Messages
74
From cold with no heating on, open hot water tap, plunger comes out of diverter valve, valve meets micro switch, switch makes, pump runs then... nothing. Doesn't go any further than that.

If the heating been on a while then warm water comes from the tap. Boiler doesn't fire though

The fact the pin is moving from the diverter freely suggests it's not that? Micro switch I've had out and tested to be sure. Coupled with the fact the pump runs I know that's ok.

Could it be the thermistor? That's where I've arrived at. Couldn't find the values anywhere to test it

Thank you in advance!
 
You'll know roughly by testing thermistors without exact values. Is there a HW thermistor on this boiler? Sounds like ignition should be happening... Good luck, had a few Simes to work on! Parts cost a small fortune, if somethings big goes I usually look to replace the boiler
 
Have you got voltage to fan ? if yes its the fan / If no check cable to fan does fan run for heating ??
 
Fan runs fine on the heating. The heating will run all day. It's just the hot water that it won't fire on.

Followed the fault finding chart to no avail. Is it a 2 sped fan?
 
Was thinking if it's a 2 speed fan then maybe the faster of the 2 has packed in. Booked to go and have a 2nd look at it tomorrow. More time spent but it's all experience isn't it
 
Probably better to speak to sime Tec wile your in front of unit so you can carry out checks and they can talk you through it could be a PCB fault
 
Update for anyone who searches this in the future.

Went back today and found when demand for heating or hot water is present and after the pump starts, the fan gets a few very short pulses of 240v, this continues with the duration of the pulses getting longer for about 5 mins before the fan eventually splutters to life. Once it's running it runs fine. The fan relay in the board however is roasting hot. New pcb is £302 from my supplier so recon ordered off eBay at customers request.

Will see how that goes when it arrives.
 
Status
Not open for further replies.

Reply to Sime ecomfort. No hot water unless heating is on in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...
Replies
8
Views
447
Afternoon. I have an issue with no water flow from any of the hot taps in the house, I can't seem to find a solution to the issue. System is a...
Replies
11
Views
359
Looking for any ideas to help. I've a Heatrae Sadia Hot Water tank, heated through Oil fired boiler (working fine). A week ago I reset the air...
Replies
8
Views
345
M
I've got a heating boiler which heats up the water in a tank located in a cupboard upstairs and then from there I get hot water & hearing. I get...
Replies
2
Views
685
Hi,

 Our heating stopped working today. We've got a Veissmann boiler that's under a year old, and an older Megaflow cylinder, and two diverter...
Replies
1
Views
705
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock