Discuss Saunier Duval Themaclassic F35E pressure issues in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
E

Ellogg

Hi All

I have searched the site for tips and advice for the above issue and followed some of the processes give by may of the members but now need a bit more advice before as need to keep heating on over Christmas and i will replace the boiler then.

My problem is get 0.8bar on digital pressure gauge, all good heating and hot water. Put heating on for and hour pressure builds up to approx 1.6bar. The over night loose pressure to 0.4bar (no hot water or heating boiler in fault) but when re-pressurizing the system it takes about 15-20 mins for pressure to build up to 0.6bar ok pressure. Also get a lot of water passing out of the reduced pressure zone valve when filling system up again seems not correct.

Suspecting PRV so as described put a plastic bag under overflow pipe outside, (this has being going on for a week or 2) found some mornings had say 2 cup fulls of water in and other days none but all time bolier pressure low.

Done check on expansion vessel again go hand down back to tyre valve and pushed pin no water came out but some air noise?? (Will need to check pressure).

I have also noticed the automatic air vent on the top of the pump has water around which has gone also left deposits of limescale around this unit could this be the issue. I also removed the screw from the top of it dried water away then switched heating on for a while then off and found the water building up in the screw hole.

I know many people are going to give "that boiler is :nono:" and "you should get a gas engineer to look at it" but would like a direction so am not charged for all kinds of parts and labour which may not be required.

Thanks Guys

Ellogg
 
Last edited by a moderator:
You need a gsr. Not a diy repair. And no, we won't give you any clues so don't pm me explaining that.

Oh, and this forum has a no swearing policy. Don't do it again
 
Status
Not open for further replies.

Reply to Saunier Duval Themaclassic F35E pressure issues in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
348
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
250
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
270
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
238
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock