ting

hi all im having trouble with a riello burner, when starting up it will just ignite for a few secounds then go out and ignite again for a few secounds etc, have checked ,solenoid,photocell,capacitor and control box all of which are working any sugestions please
 
How do you know the 4 things you have checked are working?
And why did you check the capacitor as the burner is actually starting and igniting you say?
 
I took off all 4 items and put them on another burner and it started first go as for the capacitor I was just double checking for my own peace of mind
 
try taking the bits off the other burner and using them on the duff one, normally the photocell is the issue
 
Since you put all 4 items on another burner and it started no problem, then I think I know exactly what is wrong with your burner and it is very common.
You really need to get an oil engineer in and tell them the symptoms and if they are genuinely experienced they'll sort it straight away. The boiler will need tested and perhaps serviced anyhow.
 
Since you put all 4 items on another burner and it started no problem, then I think I know exactly what is wrong with your burner and it is very common.
You really need to get an oil engineer in and tell them the symptoms and if they are genuinely experienced they'll sort it straight away. The boiler will need tested and perhaps serviced anyhow.

Oh do tell you tease :)
 
I think we'll close the thread there before there's blood.

OP, please call in a competent person before you cause irreparable damage or, worse, kill someone.
 
Status
Not open for further replies.

Reply to riello burner in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I'm looking for some advice on a frustrating problem I'm having with my old Eurostar 50-60s oil boiler please? Although it's old, most parts...
Replies
3
Views
786
I have a customers trianco burner that starts from cold ok for a few minutes (say 3minutes) then locks out then will not stay on. Boiler had not...
Replies
1
Views
642
Hi, Can I pick your brains? My boiler is often reluctant to start, sometimes it does, sometimes it seems that it will if the demand is from the...
Replies
19
Views
1K
L
Camray 5 (90A) (20 year old) oil boiler, had a noisy fan on the boiler so investigated, just a bit of dirt in the casing however, having removed...
Replies
3
Views
1K
L
Camray 5 (90A) (20 year old) oil boiler, had a noisy fan on the boiler so investigated, just a bit of dirt in the casing however, having removed...
Replies
0
Views
904
Lincoln22
L
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock