There are no guarantees with any OV system, most problems seem to arise in systems plumbed like yours where the pump is mounted high up on the flow from the boiler and very near the motorized valves (all for convenience). Mine (oil fired boiler) has the pump located in the boiler heatpac downstairs, on the boiler return.
I can run it at any pump heand or temperature I like with absolutely no problems.

You say that a increase in return temp > than say 50/55C triggers the air ingress problem.
Is the boiler up to its target flow temperature before 50/55C is reached, if not then its the flow temperature (pump inlet) which is probably triggering this, difficult to see how the increase in return temp without a increase in flow temperature can trigger a problem on the flow side at a steady temperature, the flow temperature will increase by 5 to 7C each time the boiler cycles as the burner cuts out at target temperature+5/7C, again don't know if your problems start with steady target flow temp or only when the boiler starts cycling.
Also don't like the thought of that dribble from the vent, I would think that each time this happens that you are drawing in some air each time. Of course, if the problem arises under steady, continuous pump running then another reason for the problem.
Can you ensure that the circ pump keeps running during all boiler cycling as it should only stop when both CH and/or HW is satisfied.
Also check that the pump start/stop is from the motorized valve auxiliary contacts (end switches)

You might just try (again?) running o n PP2 mode as it should run at ~ 0.5M lower head and still give sufficient flow with maybe no dribble on pump stop.

Re UPS 3 cavitation, havn't seen the NPSHr (Net positive suction head required) for this model but I would think that ~ 1.5M (like the selectric) would be OK,, the NPSHa (Net positive suction head available) however is/should be way above this as :
NPSHa is the Atmospheric pressure (absolute) + the static head - the liquid vapour pressure - the suction losses.
vapour pressure at 70C=3.1M, 60C=1.9M, & 55C=1.2M. so assuming suction loss at 0.2M (between cold feed and pump suction) and static head at 2M (use your own numbers for static head and suction losses) then the
NPSHa at 70C = 10+2-3.1-0.2, 8.7M and 10+2-1.2-0.2, 10.6M at 55C, so unless some very big problem with the suction loss at the pump (or my calcs are crap) then can't see how flow temperature itself should cause any cavitation problems so possibly points to air ingress/release at higher temps, there was a long running thread on here abut someone with problems like yours but with the circ pump located low down on the system (flow) and again couldn't be run at anything > say 65C due to noise, the system was then sealed but problems still persisted, unfortunately, the OP never told us if he ever fixed his problem.

Edit: Just saw that you had/have been running on fixed speed3? hope not for long as this is a disaster IMO with your type of system, CP1 at 3M should be a very good setting.
Morning,

I’m only running fixed 3 to see if it pushed / drew any air out of the system. PP2 mode from memory did not give me enough flow to the furthest rad in our living room when most of the trv’s had shut upstairs. I can get 12 deg drop across the furthest rad (with all trv’s removed) easily on constant speed 2 (haven’t tried constant 1) and cp1.

So, yes the boiler is already at 70 deg when this happens, I’ve been monitoring temps and it is purely driven by return temp, HW only with a cold cylinder the boiler is running with 70deg flow and has modulated down to minimum output, I adjusted the balance valve to give a 15 deg drop (measured at they cylinder) after a few mins the return temp starts to slowly rise as the water is heating, after roughly 20 mins the return temp is now into the 60’s and air is building, you can hear it going through the pump, not big glugs but lots of little bubbles. With further heating it gets worse and starts to whoosh round the system until causing the pump to cavitate.

Balance valve on the HW return is open 3/4 of a turn, this gives the 15 deg drop and doesn’t impact the CH system too bad when both are on.

Pump is controlled by valve aux contacts, same wire runs to the boiler for demand, yes the pump runs when the boiler cycles.

The boiler starts to short cycle right at the end of the HW heating, on min output the difference between flow and return is only 6-7 deg, it does all seem to happen at the same time but I think the cycling is normal?
 
Strange alright re return temp, it looks as if its releasing air on heating up as it "must" be air that's entering the pump suction, presume its not affecting something within the boiler Hx?.

When it starts cavitating, if you adjust the dT to bring the return back down to "normal" does the pump stop cavitating without you having to release any air?.

CC2 is still quite high IMO at 5.2M, suggest CC1 @ 4.2M which may run at ~ 3.8ish or CP1 which would be great if it satisfies your flow rates @ 3M. and may stop that dribbling.

Failing this suggest plugging the vent, there is already a compression fitting on it and lock open (tie wrap) any isolating valve(s) on the cold feed and see how it reacts.

1639992346453.png
 
Hi John, firstly thank you for taking the time to reply.

So, todays fun and games, I tried the pump on multiple settings, with the loft hatch open and tank lid off I can confirm that I am getting some pump over, not a vast flow but more of a constant trickle, and the circumstances effect this. Let me try to explain what i've done today.

With all rads on (TRV's removed) the system is nicely balanced, results are as follows

CP1, 12 dT on each rad, 24 Deg dT at the boiler whilst the system was warming up (max output)

CP2, 10 dT on each rad 19 Deg dT at the boiler, again whilst warming up (max output)

Furthest rad has the lockshield fully open.

With CH and HW demanding 1 turn open on the cylinder balance valve starts the pump over. With a cold cylinder I need the balance valve open 3/4 of a turn to get a 15 deg dT so this stops the pump over.

Running on CP1 I get no pump over, even with the balance valve fully open, I'm pretty sure I ran CP2 with just the HW and again didn't get pump over (guess lower flow?)

So now the system is again running CP1, I started to get air when on HW only but it is more like aerated water, not big glugs and sometimes a whooshing noise, should the air not exit up the vent pipe? or is it usual for it to get dragged round the system.

I let the HW and CH run together but just had the nearest two rads fully open (both valves) I could hear little pin pricks of air entering the rads, the pump never cavitated and the air noise eventually almost disappeared.

Could this be purely oxygen rich water entering the system? Annoyingly the air in my system collects in the pipes that run to a vertical rad in a hallway, the pipes are tapped off the upstairs flow and return and run in the ceiling and are plastic, so probably a high point, getting the air out involves draining half the rad out, then open one valve so the inrush of water brings the air with it, not ideal but the only way. My thoughts are that this process is introducing more fresh water in every time, viscous circle!
 
Last edited:
Need to add something to the post above, might have found something!

Whilst continuing to find the cause I have noticed that when on CH only I could hear a noise from the HW valve, not 100% sure if it is air being drawn in or water being pulled past, however if I fully close the cylinder balance valve the noise stops, start to open the balance valve and the noise starts again!

9 out of 10 times when the HW is demanded on a resting system I can hear a big glug of air as the pump turns on, could the HW valve be letting in air that is being trapped in the coil? I would have thought it would always be under a positive pressure but with it all being upstairs (close to the feed tank) and the pump circulating the rads could it be a negative pressure on the coil side of the HW valve?

System is running now CH only, balance valve is shut tight, boiler flow is 68, return is 52, each rad is showing around 12 dT. No air at all moving round the system.

I'm going to demand HW and open the balance valve once the Honeywell valve is open and see if I get any air, thus eliminating any negative pressure, will report back.
 
Don't think any motorized valve will/should pass when closed
The dimples look correct but check arrows on zone valves for correct orientation.
 
Valve is fitted correctly, although looking at an internal image of one the ball blocks the inlet pipe when off, so if the shaft was letting in air it would be pulled in if there was a negative pressure.

Do you think it could be under negative pressure? Could this really be the issue?

Is it feasible to test this by running the CH, opening the balance valve and loosening the lower union on the valve to see if water comes out? (with HW valve off of course)

So, the system has been running now for over an hour, CH only with 68 flow and 54 return, no air in the system and quiet. I opened the balance valve 1 turn after giving it a HW demand and left this running for 10 mins, return temp came up to 63 as the cylinder is hot, again no air at all.

As I now have all the air out of the system and it is not making air I also had no spurts of water from the vent pipe on shutdown.

Has anyone ever had a valve let in air before from return suction?
 
It's certainly worth trying the above even though with system at rest one might have expected to see some sign of a leaking shaft seal but then again maybe not as head pressure so low.
 
It's certainly worth trying the above even though with system at rest one might have expected to see some sign of a leaking shaft seal but then again maybe not as head pressure so low.
Yeah I would think the same too but I’ve seen other posts about rad valves passing air but not water, got to be worth a shot.

The head is just shy of 2m, so pretty low pressure.

Going to use the immersion for a few days with the balance valve hard closed and see how the CH performs
 

Reply to Repeated Air in Central Heating System - Help appreciated in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
196
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
292
PSxxxxxx
P
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
227
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
277
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
465
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock