Hi, I’m looking for advice about our Honeywell Evohome system. It has never been quite right & looking at info online I think the BDR91s have been installed too close together. At the moment we have a problem with the hot water connection - on the base unit it is just showing an egg timer rather than a temperature & we are unable to get it to connect so we will be running out of hot water soon. Any advice appreciated! Thank you
 

Attachments

  • A6AB38FC-E3FA-4EA6-9B41-14754A917B63.jpeg
    A6AB38FC-E3FA-4EA6-9B41-14754A917B63.jpeg
    130.6 KB · Views: 15
the stopwatch sign on hot water is temporary override
The stop watch sign isn't the override. It's the symbol when it's lost communication with the HW receiver.

HW sensor - needs good AA batteries that are reading over 1.5v. Soon as they drop below 1.5v they play up. So replace the batteries then press the button on the front once. If that doesn't solve the issue there are other things it can be.

Regarding the other issues bit of background/problems might help address these.
 
The stop watch sign isn't the override. It's the symbol when it's lost communication with the HW receiver.

HW sensor - needs good AA batteries that are reading over 1.5v. Soon as they drop below 1.5v they play up. So replace the batteries then press the button on the front once. If that doesn't solve the issue there are other things it can be.

Regarding the other issues bit of background/problems might help address these.

Thank you! It was a problem with the batteries (we didn’t even know it had batteries:oops:)
It all seems to be working fine now, thanks so much for your help!
 
According to this it is it’s all I can go off
Sorry I thought you were referring to the egg timer, I didn’t see the stopwatch in the corner.

Yes the stopwatch means a override has taken place by the user.

The egg timer means there’s an issue with communication between the panel and the CS92A
 
Sorry I thought you were referring to the egg timer, I didn’t see the stopwatch in the corner.

Yes the stopwatch means a override has taken place by the user.

The egg timer means there’s an issue with communication between the panel and the CS92A
It’s ok I didn’t notice the egg timer 😀 never dealt with evohome only had 1 customer with it
 

Reply to Problems with Honeywell Evohome system in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi I have a Honeywell ST699 programmer which is working fine but I want to learn how to decommission it (disconnect it from the rest of the...
Replies
0
Views
395
We have a Megaflo CL210 Cyclinder along with Evohome hot water kit and have come across a problem. We have had solar installed and a Myenergi Eddi...
Replies
8
Views
749
hey all, Based in South England, UK. Hope this is the correct place to ask and that ive added all the required info/images. I had an old boiler...
Replies
2
Views
1K
Hi, We moved into a new property yesterday and are a little baffled by the heating/water tank situation. The previous owners unhelpfully left any...
Replies
3
Views
374
Looking for a quick bit of advice since I'm trying to wrap my head around what work I need done. Right now I have an old conventional boiler...
Replies
1
Views
767
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock