Worcester 35 CDI two different shower valves, I of which is brand new, both showers run hot for say 5mins then start to run cold for 3-4mins then hot then cold again, no taps being opened elsewhere in house
any help please?
 
Both showers run at the same time or individual?
 
Does the boiler stay alight or does it go out as well

Also is the kitchen hot tap doing the same ?
 
Hot and cold piped up correctly to the showers ?
 
Do you know if the filters were cleaned ?

Doesn't sound like a boiler issue as the hot tap is fine
 
Sounds like a bit of cross-flow from the cold supply to the hot water from combi.
Do you have any check valves on pipes to shower valves or non return valve on hot water out from combi?
cheers,
Andy
 
Status
Not open for further replies.

Reply to problem showers from combi in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
157
We have hot water, tank for hot water why is the hot water boiling hot from tap,and shower, We are on a schedule for hot water via our hive app 2hrs in morning 2 hrs in evening Any help be much appreciated
Replies
4
Views
143
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
150
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
230
P
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
1
Views
217
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock