Discuss Pressure testing 63mm gas pipe in the Plumbing Jobs | The Job-board area at PlumbersForums.net
Bingo.........
There you go mip 75 mbar
Mop 23
So test would be 82.3 so 83mbar so you could test the mdpe at 100 mbar
Mop 23
Thanks for the calculations. As I don't have a gauge that does 100mb, I could do this as you suggested in the 1st place to 1 bar as it is only a soundness test after all. But, as you say it is commercial so should I avoid.
Well if one thing that comes out of this I have learnt a bit about cost of fittings for this size pipe and strength testing.
Thank you all
Upto you as it's not connected you could say your only testing the pipe for defective not carrying gas
Don't have one
Got a dial gauge eg pressure and an anton 140
Bes do a 100 mbar gauge
Reply to Pressure testing 63mm gas pipe in the Plumbing Jobs | The Job-board area at PlumbersForums.net