The hot & cold pipes to my bath are 15mm, shouldn't they be 21mm. The hot water is feed from a hot water tank and is a dribble whilst the cold is very strong. Should I have the pipes changed to 21mm or would an electric pump on the hot water feed suffice? If fitting a pump, are they robust and how long should they last before being renewed?
As a plumber finding this in your house, what would you do?
 
Is the tank feeding the hot water in the loft or ontop of the cylinder?
 
Are you referring to a vented cylinder or unvented? If vented then absolutely, the pipes should be larger bore, as it’s typically low pressure. If you have an unvented hot water cylinder then 15mm should be ok as it should be equal to your incoming main or pressure reduced if quite high.
 
Hi, the hot water comes from the top of the hot water cylinder. The cylinder was with the house when bought 15 years ago so I expect it'll be vented. Would a pump suffice or is it a strip out and re-plumb?
 
The pictures show the tank and the pipework to the bath. This was put in by a plumber who said it's the taps that are causing the problem. The feeder pipes rising from the floor aren't the original pipes
 

Attachments

  • IMG_2034.JPG
    IMG_2034.JPG
    366 KB · Views: 28
  • IMG_2035.JPG
    IMG_2035.JPG
    449.1 KB · Views: 24
  • IMG_2030.JPG
    IMG_2030.JPG
    432.6 KB · Views: 24
  • IMG_2031.JPG
    IMG_2031.JPG
    453.8 KB · Views: 29
Would get rid of them valves attached to the pipework that comes out the floor your flow should be a lot better with them removed
 
Thanks for photos. You have a vented cylinder, above this somewhere will be a cold water storage cistern, which the higher up it is, the better the pressure and equally flow rate. Hard to tell, but there appears to be a gate valve or 2 on the hot water from the top of the cylinder, which if not fully open, will restrict the flow. I would also be inclined to replace the hot pipe for 22mm for decent flow rate, and I would also have it separated from touching the cold pipe to prevent undue warming (water regulations).
 
You say you’ve been there for 15 years, is this a new problem?
Have you recently had work done on the system?
By the way that work under the bath has not been done by a plumber, at least not a good one.

What is that flexible pipe going through the wall with duct tape on it ? (Hopefully from a fan downstairs?)
 
The bathroom was re-fitted 5 years ago. It was a qualified plumber that I used. His response to the poor flow was, wrong taps, needed a pressurised water tank. Neither of which seemed correct. Sadly we've lived with it since and have only now decided to look for a resolution. Yes it's a fan from the downstairs shower room.
 
As Shaun, the service valves don't look to be full bore, so will be a restriction.
Also the 15mm plastic pipe is not 15mm internally, so will be another restriction and flexis' are even worse if there are any at the taps.

I'm surprised it's 15mm hot out the floor and not 22mm if it's always been vented.

Also as Undertrained, what do the taps look like, they may be High pressure (unvented) only.?
 
All the gear, shower, bath and fitting bought from the same supplier and fitted by the same plumber, I don't see how the taps could be at fault, they're bath taps with an extension shower fitment.
 

Attachments

  • IMG_2036.JPG
    IMG_2036.JPG
    181.3 KB · Views: 24

Reply to Poor flow of hot water in bath in the UK Plumbers Forums area at PlumbersForums.net