I suggest you read the Grundfos Alpha Documents.
Thanks for those very interesting and useful reading....this document section raised hopefully last questions.......
Bypass commissioning Alpha2 or 2L document
For variable speed pumps, a manual fixed bypass arrangement is recommended. I HAVE AN AUTOMATIC BYPASS FITTED (Honeywell DU144).
An automatic bypass valve should not be used with the Alpha2 pump in proportional pressure control.
I HAVE AN ALPHA 2L CAN IT BE USED WITH PP CONTROL?
IF NOT SHOULD I PUT IT BACK TO CP2 OR JUST SPEED 11 PERHAPS
For condensing boiler, the operation of an automatic bypass with proportional pressure control is counter productive to maintaining condensing boiler efficiency at high load conditions. As the pump pressure increases, the bypass flow will also increase which
raises the boiler return water temperature and reduces boiler efficiency.
In constant pressure operation a fixed manual bypass for will maintain a constant bypass flow.
WHAT ABOUT THE ‘BYPASS RADIATOR AND A TRV?
Many thanks for your help to date..John