So I've just done some jug filling tests with times and temps. Not one room upstairs gets above 42c
Kitchen tap (closest to boiler)
12.09 secs @ 42.4c
18.10 secs @ 54.4c
Bathroom ensuite
12.82 secs @ 39.4c
20.31 secs @ 43.1c
Main bathroom sink
12.51 secs @ 35.1c
21.83 secs @ 41.1c
Bath
4.13 secs @ 31.8c
11.43 secs @ 39.1c
13.07 secs @ 39.9c
13.47 secs @ 41.2c
17.68 secs @ 41.7c
18.94 secs @ 41.6c
21.62 secs @ 41.2c
Flow Rates & Boiler Outputs based on data above: assuming cold mains at 9C
12.09 secs @ 42.4c 4.96LPM, 11.6kw
18.10 secs @ 54.4c 3.31LPM, 10.48kw
Bathroom ensuite
12.82 secs @ 39.4c 4.68LPM, 9.93kw
20.31 secs @ 43.1c
Main bathroom sink
12.51 secs @ 35.1c 4.79LPM, 8.72kw
21.83 secs @ 41.1c 2.74LPM, 6.14kw
Bath
4.13 secs @ 31.8c 14.52LPM, 23kw
11.43 secs @ 39.1c 5.24LPM, 11kw
13.07 secs @ 39.9c 4.59LPM, 9.9kw
13.47 secs @ 41.2c 4.45LPM, 10kw
17.68 secs @ 41.7c 3.39LPM,7.73kw
18.94 secs @ 41.6c 4.68LPM, 9.93kw
21.62 secs @ 41.2c 3.17LPM. 7.12kw
Reply
Looks like the flows are too low or there is a flow switch problem as the only output that looks like a constantly firing boiler is 4.13 secs @ 31.8c 14.52LPM, 23kw
I think the minimum output of this boiler is 8kw?? so requires a minimum flowrate of 2.25LPM to avoid temperature exceeding 60C, flow switch possibly set to 3/3.5LPM???perhaps faulty??. There is certainly a boiler problem somewhere IMO.