Yes, that's exactly what I mean, a straight by pass between flow & return. I wonder was the system first conceived with the mid position valve only which I think is not allowed with a unvented HWC as it will power fail to hot water.
I may not have made myself clear. I wasn't saying that a minimum flow was unnecessary, but that it did not need to be the same as that specified for full ouput. A 24kw boiler with a 20C differential has a flow of approx 17 litres/min. If the same flow is maintained when the boiler has modulated down to 6kW, the differential will be only 5C. Whether that is a "good thing", I don't know.Quite a lot of boilers, if not the majority, will not modulate below 5 kw, there two reasons, IMO, why a minimum flow rate should be maintained, one is, to avoid thermal stressing of the HX, if one allows say 25C delta t, then a flow rate of - 3LPM. The other reason is more practicle, if the delta t is too high then the boiler will very quickly cut out on high temperature (SP+5) especially on start up when the boiler output can be at 75% during the ignition phase.