Good morning,

I'm trying to get an MCZ Hydro-22 pellet stove to provide heating. The stove is operational and is providing hot water to the taps, but it is not supplying the radiators.

Things I have done:

1. Bled radiators
2. Re-pressurised system (all gauges showing 1.5 bar)
3. Set thermostat to 30
4. Checked electricity to pumps (the lights are on in the diode in the switches) and there is heat on both sides of the pumps (Grundfos) - but there are no power lights on the pumps and pressing the button on them doesn't do anything.

I spoke with someone who suggested that the pumps may have gone, or I need to open a valve somewhere in the system. I've tried a number of valves (returning them to their previous positions after a few minutes).

[This system is at my mum's business in the highlands - she's in hospital - and the installer is now out of business and other engineers are hard to come by, so I'm turning to the internet as a final hope before I make an expensive call to an engineer from some distance away]

Any help greatly appreciated, I've put some photos on from the boiler room at the back.

Thanks
Jake

IMG-20181107-WA0001.jpeg


IMG_20181107_122236.jpg


IMG_20181107_122226.jpg


IMG_20181107_122247.jpg
 
Is there a programmer / timer?
Is it that on the board near the top under the switch and socket?
Is it set to ON or Auto and is the time correct?

Post a photo if you locate the programmer
 
I would look for a 3 way valve not shifting from Dom hot to Dom hot and ch , it’s not rocket science, a local fella can check this dead easy, do not be baffled by cow poo. centralheatking
 
Thanks both for replies - the programme is set to P01 (which from the manual means on pretty much all the time.

I've taken pictures of all programme settings I can find - there is hot water, so I can only assume its doing what its supposed to, but hot water is not entering the central heating loop.

I'm sure it's an easy fix, but we are in the middle of nowhere and getting someone to come look is a big effort

IMG_20181109_112616.jpg


IMG_20181109_112550.jpg


IMG_20181109_112500.jpg
 
Ok ,then see if there is a manual override to th three way
Unit, you could try setting it to change back and forth, and I would give it a sharp smack with a wrench , it is probably stuck Chking
And give it a dose of wd40 plenty right down he holes by the lever,
Plenty mind you, let it penetrate for an hour or so smack it again,
Then see what happens , let me know Centralheatking
 
Set them to on and gave them a thwack with a wrench. The lights on the Grundfos pumps came on, but pressure on the guage went up to above 2.

Going to bleed the radiators again.

Also the switches on the honeywells dont feel sprung and aren't locking into the on position. Suppose that means they need replacing?
 
Is the lever loose or does it take some force to move it ?
 
Lever is loose, but does not lock into the open position.

The electrics on it seem to be working fine. I can hear and see them changing when I change heating to off / on

Took the electrical unit off. There is very little movement on the valve adjuster (maybe 1/3 turn) does it need to be more than this?

IMG_20181109_132320.jpg
 
No that's fine

Does the pump turn on when you manually lock it open
 
Do you have a multi meter?
 
Only when there's call eg the port valves open
 
So if I'm not getting any lights, even when the system should be working and I'm pressing the grey arrow button then its probably an electrical issue to the pumps?

Yea sparky who knows heating systems should be able to help
 
Post no. 8 you said when you set them (valves?) to on, the pump light came on?

Did you hear or feel water move around the pipework?

To latch the valve in manual, push the lever across to on, then push it down into the wider part of the slot that's got the tooth like part on it.
Hold there for a second, as the spring tries to reset the valve it should latch on. (to release push lever up to the longer part of the slot.)
Does the pump stay on?
 
I may know a guy if you get stuck
 
Ok ,then see if there is a manual override to th three way
Unit, you could try setting it to change back and forth, and I would give it a sharp smack with a wrench , it is probably stuck Chking
And give it a dose of wd40 plenty right down he holes by the lever,
Plenty mind you, let it penetrate for an hour or so smack it again,
Then see what happens , let me know Centralheatking

You are kidding right?

I take it you know this guy well and are kidding him along? Well I bl00dy hope you are.

Let's just spray a petroleum based fluid into where a freakin electric motor using brushes sits ! Sorry, but what the hell are you thinking Rob? At the very least, WD40 will start attacking the plastic gears. At worst you start a small fire...

Sorry, but that's just bl00dy irresponsible.
 
You are kidding right?

I take it you know this guy well and are kidding him along? Well I bl00dy hope you are.

Let's just spray a petroleum based fluid into where a freakin electric motor using brushes sits ! Sorry, but what the hell are you thinking Rob? At the very least, WD40 will start attacking the plastic gears. At worst you start a small fire...

Sorry, but that's just bl00dy irresponsible.
The unit is probably stuffed anyway so a squirt will not make things any worse , that’s my opinion and what I would do if it was my gaff....centralheatking
 
I didn't end up spraying them - took the covers off and watched them as they switched on/off - both two way valves are working fine by the look of them.

The only thing I cant work out is why the pumps aren't pushing water around. As I said earlier they did light up - but haven't done since. I've been around the place, set the thermostats up/made sure that every switch I can find is set to on - made sure that the return valve on the heating loop is open etc etc.

Completely stumped.
 
Can you see the micro switches working in them ?
 
I didn't end up spraying them - took the covers off and watched them as they switched on/off - both two way valves are working fine by the look of them.

The only thing I cant work out is why the pumps aren't pushing water around. As I said earlier they did light up - but haven't done since. I've been around the place, set the thermostats up/made sure that every switch I can find is set to on - made sure that the return valve on the heating loop is open etc etc.

Completely stumped.
Ok , we all need to fault find on his one, r u sure the pumps are actually pumping , often when they are bust,seized the impellor head will rotate but no liquid wil be moved , sorry about underlines I do not know how to switch them off

Chk
 
I didn't end up spraying them - took the covers off and watched them as they switched on/off - both two way valves are working fine by the look of them.

The only thing I cant work out is why the pumps aren't pushing water around. As I said earlier they did light up - but haven't done since. I've been around the place, set the thermostats up/made sure that every switch I can find is set to on - made sure that the return valve on the heating loop is open etc etc.

Completely stumped.
Is there voltage to the pump? When the valves have motored?
 
My take on the problem......

Those grundfos pumps are absolutely Rubbish, they were a quick and late design to get on the modulating pump market. Whip it out !!!!

The leds will be lit, but the actual performance will be far under.
 

Reply to MCZ Pellet central heating system in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
408
Hi everyone. I'm currently working on a job for a customer. their radiators are not all heating up. in total there is 12 radiators. 4 of these are...
Replies
1
Views
541
  • Sticky
I thought I'd create a master thread to move all of these similar threads into, over time like. If your central heating doesn't work boiler...
Replies
8
Views
1K
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
331
PSxxxxxx
P
  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...
Replies
8
Views
464
Back
Top