Out of curiosity, what the norm for lpg analyser reading on a new boiler. Commissioned my first lpg new install on a heat line combi (not my choice) and once I converted it and took the readings, everything seems high but the co2% is spot on.
381ppm, 0.0037ratio
Now I thort maybe there's a problem but I fitted 2 next to each other and the readings are identical. Is this a normal reading?
MI's state no higher than 0.004 and co2% 10.3 +- 0.3 so it is in but only just and im not used to seeing high ppm's.
Just got my lpg ticket if you didn't realise.
Thanks in advance.