had a leaking prv on a vokera boiler so valve is a 3 bar blow off
took out old one and scaled up and put new prv head in but system still loosing pressure and leaking from prv i am told by customer
as its 3 bar spring in there cant see how it can still be leaking
any ideas appreciated..tks
 
re pressure/check expansion vessal,i,m haveing fun and games with a mystery leak
 
that was my next thought prob is vokera put them on the back of the boiler..but i had it running at 2bar no probs so not sure why is dumping it out other than making a cup of tea and sitting there for the evening
 
There have been a couple of similar posts and my boiler/system is doing the same.

What I think is happening is that the expansion vessel has lost its charge or the bladder is leaking. So when the boiler fires the expanding water has no where to go and is discharged from the PV. When the system cools down the pressure drops and the boiler will not fire. This has the symptoms of a leak as when you top the system up the pressure will again be lost on the next heat up cool down cycle.

I have a system boiler and to avoid having to strip the boiler down to fit a new vessel inside the boiler will be fitting an external pressure vessel.
 
if the new prv is opening at 2bar i would say the pressure guage is faulty and your exp vessel needs recharging / replacing
 
Try running the heating at maximum temp, you should soon see the pressure gauge rising to 3bar. This indicates the vessel need charging, when cleaning the PRV make sure you clean the inside of the valve as well. You get bits of sludge on the seating which can sometimes stop you getting a good seal.
 
Status
Not open for further replies.

Reply to leaking pressure relief valve in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and plasterboard celling. I have got unvented pressurized RM Cylinders hot water system with 27KW Worchester gas boiler with expansion vessels . When...
Replies
2
Views
471
losing pressure
L
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem could be. We have a biomass boiler and stratification tank set up and recently had an issue with boiler pressure dropping off when the system was cold...
Replies
9
Views
365
Hello, I live in a two floor semi with a gravity fed conventional gas fired boiler (Potterton Kingfisher MF). The boiler is fed cold water from the loft water reservoir tank (which also feeds the cold water taps in the bathroom & the WC cistern). There is an expansion vessel attached to this...
Replies
0
Views
497
I have a Vaillant eco plus 837, year installed 2008. It works well. We have one large zone for the house with 13 rads running off it. We also have an UFH zone in the kitchen. Near the boiler I have 2 port valves which control this part of the system. The boiler has been loosing pressure...
Replies
1
Views
307
Hey, I've got a Grant Vortex that's leaking water from the seal around the expansion vessel - it's the round type about 50cm wide. The system is at 1.5 - 2 bar, but the expansion vessel has no air in it, and it's leaking water. No water is coming out of the Schrader valve either. The system...
Replies
2
Views
1K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock