Hello chaps,

i came across a 'lag lead' system.
ie two heat only boilers working together to heat up a whole house and provide hot water via two indirect hot water cylinders.
The boilers are keston 28.

the lag lead is controlled via three switches which im not sure what they do. I.E one makes the 1rad symbol appear, another makes 2rad symbol appear.
has anyone installed on like this and if so what do the three switches do?

cheers
DD368
 
I haven't been involved in one of these for a while, but my (very limited) understanding is this.

Your lead boiler comes on first when there is demand. If it can satisfy the demand alone, thats fine. If it can't satisfy it, the lag boiler comes on to support it.

There is usually/sometimes a sequencer switch that reverses the lead/lag in order equalise wear on the boilers, so if you start with Boiler A = lead, boiler B = lag, the sequencer changes it to B=lead, A=lag.

Do you have a pic of the three switches?
 
We're the kestons on a jig from the manufacturers into a low loss header?
 
I haven't been involved in one of these for a while, but my (very limited) understanding is this.

Your lead boiler comes on first when there is demand. If it can satisfy the demand alone, thats fine. If it can't satisfy it, the lag boiler comes on to support it.

There is usually/sometimes a sequencer switch that reverses the lead/lag in order equalise wear on the boilers, so if you start with Boiler A = lead, boiler B = lag, the sequencer changes it to B=lead, A=lag.

Do you have a pic of the three switches?

Pretty much covers it!
 
Status
Not open for further replies.

Reply to Lag Lead System??? what is it? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
I have a factory lagged indirect hot water cylinder in the airing cupboard, installed about 2002. The control thermostat is fitted near the...
Replies
14
Views
1K
Hello, I live in a two floor semi with a gravity fed conventional gas fired boiler (Potterton Kingfisher MF). The boiler is fed cold water from...
Replies
0
Views
530
  • Question
My disabled daughter’s hot water has stopped working. It’s a relatively modern Potterton boiler with an indirect sealed hot water system and a...
Replies
12
Views
947
Hello, We had an extension built seven years ago. Initially the builders' plumber connected the heating to the house system but this didn't work...
Replies
23
Views
842
I have a Worcester Greenstar gas boiler circa 2017. There has been a noise coming from the boiler which resembles running water, I have checked...
Replies
2
Views
201

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock