safeplumb

Hi Guys can you help,

I had to recently drain down my Ideal Isar HE24 boiler to fit a new drain off tap on the heating return pipe which was leaking. Refilled and everything is working fine except for the pressure guage which reads 3 bar when the heating is running, when the heating goes off it stays at 3 bar. If I drain out some water till the pressure guage reads 1 bar and then rerun the boiler the pressure guage eventually goes up to 3 bar again and stays there when the heating goes off. Did not have this problem before I drained down to fit the drain off tap. Any ideas?

Cheers Al
 
Sounds to me like you filling loop is passing
 
:iagree: as above :)

Disconect the loop and see if it's passing, you want to hope it is to be honest :)
 
I would say it needs the expansion vessel recharged the only reason it is stopping at 3 bar is because the PRV is working properly.
 
I would say it needs the expansion vessel recharged the only reason it is stopping at 3 bar is because the PRV is working properly.

If it were the exp vessel the pressure would go down when the heating cooled would it not? The exp vess theory does not explain how it rises to 3bar and stays there alas! There may be an issue with the exp vess but that'd have nothing to do with why the pressure is returning to 3 after the pressure is dropped as the op has mentioned. Would you agree?
 
I have seen the pressure going to 6 and the PRV opening to allow the release. It will only go back to 3 and sit there because thats what the PRV is set to. I, in my opinion would open the valve and recharge it anyway and that would let you see immediatley if the Vessel is faulty.
 
Of course the loop is a very valid and probable possibility. cant see the trees for the fuzz caused by last nights beer!!
 
I have seen the pressure going to 6 and the PRV opening to allow the release. It will only go back to 3 and sit there because thats what the PRV is set to. I, in my opinion would open the valve and recharge it anyway and that would let you see immediatley if the Vessel is faulty.

I would of said that by doing that you stand a higher risk or tearing the diaphragm

There is deffo a passing valve or a broke plate he

Your theory is wrong.
 
I meant open the PRV valve and recharge the vessel but as the guys have said it is most likely a passing loop.
 
Status
Not open for further replies.

Reply to Ideal Isar High Pressure Guage in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
126
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
231
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock