Hi All after some advice. Called out to a boiler with a noise(didn't do it when I first got there), reverberating noise on low rate. It was also due a service, checked and cleaned condensate( and pipe), cleaned heat exchanger,(replaced burner as deflection in the plate), replace spark/flame electrodes, clean injector/venturi, all readings checking out. Ideal told me it needed a new fan(fitted it still same problem), only think I haven't dismantled is the flue, elbow facing you at front of boiler(unable to access clamping screw(new build and think it was put in and then rotated)). so elbow toward 90 elbow on it's side facing left with length of flue out wall....all looks good looking into the flue from outside(no visible blockage)......they then told me I needed to redo condensate(WTF)....poured loads of water into outlet in boiler.....drained well. cut section of rigid pipe out under sink....wet vacced and co2 cannister blasted down there....all seems good. Any constructive advice appreciated. I don't think I have forgot anything.
 
I think you have covered the obvious things.
Maybe try the condensate into a bucket for a few days to rule out back pressure building up
 
Gas valve
 
Gas valve
Said this to Ideal as I have changed quite a few on Logics that are off the scale on minimum, but spot on max.....they said it won't be the gas valve apparently. I think I have one(new) in the garage....may just put it on and try it.
 
What are your reading's when it's on Low Rate?

You're either not getting enough flow through the burner or as Shaun says Gas valve. However when the gas valve is faulty i've usually had readings off the scale on low rate.
 
What are your reading's when it's on Low Rate?

You're either not getting enough flow through the burner or as Shaun says Gas valve. However when the gas valve is faulty i've usually had readings off the scale on low rate.
readings all check out on low rate(had them before where it maxes out on low...but fine on max.
 

Reply to Ideal Heat H18 in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to...
Replies
9
Views
351
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
301
PSxxxxxx
P
P
  • Question
Boiler is SIRIUS THREE FS 70 Potterton commercial. Situation: We are small building contractors and my labourers managed to damage the radiator...
Replies
2
Views
148
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
564
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock