O

oldbod

Hi. Wonder if anybody can help me with this please? Consultants are redesigning the heating for the Church where I work, they're working to an available heat output from the boiler, an Ideal Concord C Series 2 330, of 330,000 btu. That's what our 30+ year old handwritten records say.

The rating plate from the boiler is missing, but I have a nagging suspicion that this unit has an output of about 70kWh. A continuous burn shows the unit currently consumes a cubic meter of gas in about 410 seconds, which seems to be equivalent to about 100kWh... / 330,000 btu input. I don't know if there's any way this is adjustable much, but can't see why we would have had it set much below maximum even if it was.

I haven't been able to find an answer anywhere online, so if anybody here can tell me that would be really great.
Thank you very much in advance for any help
 
Yeah, that's 100.1kw.

Which is about 341,541.2 btu.

Your net output would actually be closer to 307,417.82 btu or 90kw.
 
Last edited by a moderator:
Input is what the boiler will consume and output is what the boiler gives to water. Deduct one from the other and you have efficiency.
Your figures seem correct.
Your new boiler, depending on the building! Will have an input closer to the output of the old one. As it will be more efficient.
 
Thanks very much for the replies. Very much appreciate your taking the time to help me. I think I probably didn't phrase the question very well, 4am isn't my best time, you can tell I was worrying!

We aren't replacing the boiler, only the distribution side.

My worry is that I don't know for sure if the 330 in the boiler designation is energy input or rated output...
 
Status
Not open for further replies.

Reply to Ideal Concord C series 2 330 rated output in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
155
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
319
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
288
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
375
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
213
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock