The front diaphragm doesn’t control the pump the rear one does
 
That’s the pump proving one so providing your info is correct should fix your problem or it’s a weak pump
 
Sorry, I have one last quick question, when I replaced the DHW diaphragm, I just turned the Mains off and ran the hot tap until there was no more water. Am I able to do the same when replacing the CH diaphragm or do I have to drain the boiler?
 
Have to drain the heating system if your upstairs and above the radiators only need to drain the boiler but if your downstairs need to drain everything above the boiler
 
Have to drain the heating system if your upstairs and above the radiators only need to drain the boiler but if your downstairs need to drain everything above the boiler
Thanks for all your help, so just so I am clear if you are replacing the DHW diaphragm you just need to turn mains off and run tap but if you are changing the CH diaphragm you have to drain the boiler? I will also get some fernox inhibitor when I do drain it down
 
Correct and anything above the boiler
 