Discuss Hot Water Tank Expansion Vessel Question in the UK Plumbers Forums area at PlumbersForums.net

Are you g3 registered as your working on an unvented?
 
The PRV I am referring to is the pressure reducing valve, the cylinder PRV is the pressure relief valve (safety valve) the other PRV that you refer to is probably the expansion valve and as its set to 4.5bar it might lift if you set the EV prechargeto 3bar. Have you got a pressure reducing valve installed? and if so check its setting.
Ah. The one in the combination valve. Got it. There are 3 valves in total then.
Two in the combination valve. A PRV at 4.5 bar (blue cap) and the reducing valve which connects to the supply.
I presume that's limited to the supply pressure or there about.
One PRV in the tank at 6 bar.
 

Attachments

  • IMG_20201211_104128.jpg
    IMG_20201211_104128.jpg
    382.8 KB · Views: 16
  • IMG_20220319_095453.jpg
    IMG_20220319_095453.jpg
    258.1 KB · Views: 16
I'm not. But the guy who is supervising the job is.

And what does he say set the pre charge to ? Also why are you changing an expansion vessel on an newer cylinder?
 