Typically heating misbehaves just as it starts to get cold!
Boiler: Vaillant Eco-Tec 24kw. 8 Rads, 2 towel rails.
Boiler set on max, flow piping hot out of boiler, return cold. With all rads open both sides, next to no heat. Balance rads right down, still only tepid. Operate one at a time, heats up ok.
Flushed & refilled, no apparent blockage as individually each rad gets hot. More than one, barely warm.
Boiler fires for a minute or so but goes back to standby quickly & before return is warm.
Status screen says pump operational & it seems to be running. Blocked or inefficient maybe?
No problem with DHW just the heating side. Should add that system just a couple of years old, all was ok when heating last used around June & no modifications since. Pipe sizes seem ok with 22 copper up to 4.5m from boiler thereafter in 15 hep, very few elbows etc.
At a loss & freezing! Any advice much appreciated. I have had a look through the similar threads without success thus far.
 
Coys you must be a well versed in Ch to post such a technical explianation of your problem

- maybe the mods can determine if it ok for us to quote help CHK
Typically heating misbehaves just as it starts to get cold!
Boiler: Vaillant Eco-Tec 24kw. 8 Rads, 2 towel rails.
Boiler set on max, flow piping hot out of boiler, return cold. With all rads open both sides, next to no heat. Balance rads right down, still only tepid. Operate one at a time, heats up ok.
Flushed & refilled, no apparent blockage as individually each rad gets hot. More than one, barely warm.
Boiler fires for a minute or so but goes back to standby quickly & before return is warm.
Status screen says pump operational & it seems to be running. Blocked or inefficient maybe?
No problem with DHW just the heating side. Should add that system just a couple of years old, all was ok when heating last used around June & no modifications since. Pipe sizes seem ok with 22 copper up to 4.5m from boiler thereafter in 15 hep, very few elbows etc.
At a loss & freezing! Any advice much appreciated. I have had a look through the similar threads without success thus far.
 
Has it been commissioned to MI
Well versed maybe, but always willing to listen & learn even after 30 years in the building industry.
Yes, of course it has been commissioned. It is originally a BG installation, now out of the guarantee period as system was fitted for the previous owner of my current house. The only modifications being towel rails for rads to the bathrooms up & down, single to double in hall & moving a bedroom rad locally to make room for furniture.
My post was based upon my own knowledge/experience, & the varied advice of colleagues within the trade. 4 heating engineers = 4 differing diagnoses (balancing, blockage, sludge/scale, pump) = problem unsolved. Hence, turn to the fountain of all knowledge (the web) & maybe someone has an alternate opinion.
It's not a massive drama, but I didn't realise it was so closed shop.
 
I'd go with your last mates idea, has anyone whipped it out & had a look at it's condition ??
Tomorrow hopefully, but it looks favourite so far, as all other touted solutions have been a dead end. We are a major hard water area, aided but not totally cured by Sentinel CombiGuard so it may be a factor on pump output, though to be fair little evidence of build up when flushing or in the scale reducer. Cheers for the input.
 
Ecotech it will be a lazy pump, it's hard to picture the system design but if the installation has once worked and nothing has changed I would change the pump 1st.
 
Check system pressure....
Had a couple of jobs presenting similar issues. Changwd pump on first one to no avail. Turned out pressure guage was stuck on 1.5 bar but was not working. Actual pressure way less and giving impression of lazy pump
 
If it is pressure prob on a UF screed job KayJay, suggests a fundamental problem.
 
Check system pressure....
Had a couple of jobs presenting similar issues. Changwd pump on first one to no avail. Turned out pressure guage was stuck on 1.5 bar but was not working. Actual pressure way less and giving impression of lazy pump

Good shout. Not pump - renewed with little improvement
 
System pressure a good shout.
Not pump - renewed with little improvement.
 
Apologies for duplicate post.
Not pressure either.
Powerflush as well as new pump yesterday. Double checked all TRV pins & lockshields.
Unit still stuck in a sequence thus.
From cold; fires & runs hard, 22 flow heats quickly well beyond first tees @4m+ (suggests carcass ok) Rads start to warm in sequence.
5-10 mins; boiler falls back to standby & starts cooling. Rads not hot, return barely lukewarm. Screen temp falls from 78c to 50c, & so it continues without the rads ever getting more than warm & return tepid at best.
No weather compensator etc, but could it be a rogue sensor causing micro cycle
 
Have you got a return valve with a mesh screen in it? Possible partial blockage.
 
Could be as simple as putting some airpips on the drops seen this before plenty of times
 
Status
Not open for further replies.

Reply to Hot flow, tepid return (again) in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
155
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
208
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
235
P
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
319
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and pebbles!) We saw that the pipe that takes water down the gutter was visibly full to the top. He said he will return with a coil to push through...
Replies
2
Views
114
S
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock