went to a job today , heating not working , anyway fault was found as a faulty programer, but anyway, it was a solid fues system with gravity hot water and pumped heating with a indirect cylinder, the cylinder was piped up in 28mm and heating in 22, there were 2 stats on the gravity , one high limit on the hw flow set to 80oc and low limit on the hw ret set at 40 oc , cananybody tell me excactly what these do , there was also a room stat but no cylinder stat, and no motorised valves, there was an electrician on site, but he didnt know how it worked.............!!! also has anybody got a decent wiring diaram fo one of these?? thanks guys as always!!!
 
Pump held off until temp = 40 or greater

Pump enabled at 80 or over regardless of any other control
 
STAT DRWING.jpg

stats wired as above, hi to run pump when stove is getting to hot, low to mek sure pump doh run untill primary/gravity return is warmed up, this stops thermal shock inside the heat exchanger (pumping cold water into hot exchanger) which can cause bad corrosion.
 
cool , so its quitet easy in a way then ist it! thats for that lads! much apreciated!
 
Status
Not open for further replies.

Reply to hi- low limit stats in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock