Morning all,

Struggling to resolve a problem. Back to back WC's in a fourth floor flat and the waste from toilet A(main bathroom) transfers into toilet B (ensuite) we have installed the McAlpine ARB 1 anti-cross flow valve on each side but it has only stopped solids and there is still some fluid getting through.

I have attached images of how this looks. How would you advise we fix this?

Appreciate any advice.

Many thanks,
Jack
 

Attachments

  • ensuite 1.jpg
    ensuite 1.jpg
    118.5 KB · Views: 29
  • ensuite pipe connection to main.jpg
    ensuite pipe connection to main.jpg
    168.1 KB · Views: 30
  • main 2.jpg
    main 2.jpg
    67.3 KB · Views: 31
  • main stack pipe.jpg
    main stack pipe.jpg
    110.9 KB · Views: 31
  • main.jpg
    main.jpg
    71.9 KB · Views: 30
Sorry to say not easily. Both outlets would ideally drop in a near horizontal float to the stack. It was refreshing to see he has used a 45 branch but it is so close to connecting we you are asking for problems. Not straight forward to recover from.
 
If you can, lower the branch on the stack - but it looks as though you can’t.

If you can’t lower it.

Change the branch to a double corner branch and run each wc separately back to it (this is one where the two branches are at 90 degrees instead of the more usual 180.

I’m assuming as it’s a flat you can’t drop one of them through the floor and connect to the stack lower down - you could if the services all run in a common, accessible cupboard as they sometimes do......
 
Especially given the 45 branch and it's distance from the ensuite pan, I'd say there's a partial blockage in the branch pipe (with the white collar) or in the stack if there are no flats higher.

There would have to be quite a build up to get fluids to flow back to the Ensuite pan.
I think I'd cut a rodding eye into the branch near the stack junction to watch the water flow when flushed.
It may be usefull in the future if there's any blockages.
 
I think you could well be right as assuming the toilets were not going to be put elsewhere, the plumber has done the right thing and the best they can given the setup. I would have not expected any noticeable cross flow looking at how it's been connected up.
 
uming the toilets were not going to be put elsewhere, the plumber has done the right thing and the best they can given the setup. I would have not ex
If you can, lower the branch on the stack - but it looks as though you can’t.

If you can’t lower it.

Change the branch to a double corner branch and run each wc separately back to it (this is one where the two branches are at 90 degrees instead of the more usual 180.

I’m assuming as it’s a flat you can’t drop one of them through the floor and connect to the stack lower down - you could if the services all run in a common, accessible cupboard as they sometimes do....

Do you mean like this one? Seems a good idea! hmmm
 

Attachments

  • Capture.PNG
    Capture.PNG
    72 KB · Views: 13
Is there much fall on the horizontal pipe? Sounds like isn't flowing away correctly, especially if you were having solids go back into the pan.
 

Reply to HELP - Back to back WC's issue with cross flow in the USA area at PlumbersForums.net

Similar plumbing topics

Hello, recently our boiler stopped working properly, causing a lack of heat in our 14-radiator splitter in 3 storeys. having only one boiler at...
Replies
4
Views
437
Hello everyone Here's one for you..... We have a DIY ensuite (put in by previous owners). Miles from waste stack, so SaniPro services toilet, sink...
Replies
10
Views
3K
We live in a terraced row (SW London) and our neighbours are currently in the process of finalising their extension. There is a potential...
Replies
5
Views
2K
Morning - I am after some advice if anyone can help at all. 3 days ago after 2 weeks on holiday we can home to find a sewage leak in our flat. The...
Replies
6
Views
1K
0
Hi, I live on the first floor of a 6 storey block of flats. For months now, there has been a bad smell coming from the stack pipe - the smell...
Replies
1
Views
2K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock