just a a quick background, hot water used to take a long time to come through.
while doing bathroom, found this to be because boiler 15mm hot water outlet was T'd into original 22mm pipe from when it was a gravity system.

all 22mm pipe replaced for 15mm and piped directly back to boiler... This improved times it took for hot water to come through and gave improved pressure also.

then thermostatic mixer shower was installed, and hot water went back to being slow to come through.

identified the problem, when hot water tap is turned on, the pressure drop in hot water pipe is far greater than the cold so it starts back feeding. Going to fit a pressure equalising valve with inbuilt non return valve to fix this... However I want to fix the root cause of the hot water pressure drop. Also removed a further additional isolator valve from boiler cold feed which improved pressure slightly further.

static pressure was 4 bar, dynamic pressure on cold with shower on full is 2.8-3.0 bar.
however dynamic pressure on hot is 1.8-2.0 bar! 2 bar drop from static and 1 bar less than cold. Which is why the back feeding is occurring... It's also a lot lower because I suspect that a venturi effect is occurring and the hot water is being sucked through the pipe.

so would seem there is still some kind of restriction on the hot water side of things on the boiler.

couldnt find an inline filter, so would I be correct in assuming it's a possibility that the secondary heat exchanger is scaled up? And that the limescale is causing an internal restriction?

i know it has a heat exchanger problem being sludged up as it's going hot and cold also, but that wouldn cause a restriction on cold water side, only heating side... So it maybe scaled up as well.

but either way there must be a restriction somewhere for dynamic pressure to drop 2 bar! At most I would of expected same drop as cold water.

Thanks in advance.
 
Status
Not open for further replies.

Reply to Heatline S24 hot water pressure problem. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
202
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
205
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
268
PSxxxxxx
P
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
281
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
425
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock