Hi again everyone

Just about finished all my heat loss calcs with Stelrad Stars.

I just wondered about the ventilation / air changes. These significantly affect the heat requirements.

Currently they are set as the following changes per hour :

  • Living Room - 3
  • Drawing Room - 3
  • Dining Room - 2
  • Hall - 2
  • Kitchen - 3
  • Utility Room - 2
  • Landing - 2
  • Bathroom - 3
  • Bedrooms - 1.5
All the upper floor rooms have double glazed windows. The ground floor rooms are mostly single - weatherstripped - soon to be double glazed. Ground floors are suspended timber. Living & Drawing rooms have open fires with requisite chimneys.

Are these air changes per hour about right?
 
without checking my notes i think i normally allow 3 for rooms with extract fan and 1.5-2 for other rooms. Its been about 8 months since i have done long hand calculations tho.
 
Hi again everyone

Just about finished all my heat loss calcs with Stelrad Stars.

I just wondered about the ventilation / air changes. These significantly affect the heat requirements.

Currently they are set as the following changes per hour :
  • Living Room - 3
  • Drawing Room - 3
  • Dining Room - 2
  • Hall - 2
  • Kitchen - 3
  • Utility Room - 2
  • Landing - 2
  • Bathroom - 3
  • Bedrooms - 1.5
All the upper floor rooms have double glazed windows. The ground floor rooms are mostly single - weatherstripped - soon to be double glazed. Ground floors are suspended timber. Living & Drawing rooms have open fires with requisite chimneys.

Are these air changes per hour about right?

i use 1.5 for every room
 
Slight tongue in cheek remark but don't these figures get thrown out of the window when the windows are open? And if it's blowing a gale ...
 
Would two changes suffice for the rooms with open fires (chinmeys) and suspended timber floors with plenty of underfloor ventilation?

The house by the way is a victorian semi with 10ft ceilings - and a bit draughty here & there - though I'm attending to that as best I can with weatherstripping etc.
 
Lol. Just to add. New builds should have an air change of 0.5 per hour !!!!
 
1.5 should be fine, the size of the room is part of the calc in a different area so no need to compensate here as well
 
Status
Not open for further replies.

Reply to Heat Loss Calcs - Air Changes in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have a home with an oil boiler in a garage turned into a flat, heating both flat and main house, running c plan with two pumps, two motorised...
Replies
0
Views
410
My landlord's great at getting all the Scottish government funding that's going, and there's full insulation, double glazing, an airsource heat...
Replies
4
Views
532
Hi all, I wanted to ask a general question about an underfloor heating system our plumber is proposing and if this solution will be sufficient...
Replies
1
Views
473
Hi All, I'm trying to work out why the 'rule of thumb' is ~3 radiators on a single 15mm run... I've calculated the heat demand of my house at...
Replies
12
Views
2K
I have a 320 sqft double storey house with 6 bedrooms. The house is serviced by two heat only boilers (non condensing); a 120k btu (35kw) and a...
Replies
17
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock