Hello, I have just had my 15year old Grundfos UPS 15 50 replaced with an Alpha 1 and the Alpha 1 seems quite a bit noisier than the the old one,
I have a new UPS3 sitting in a box and I am thinking of changing the Alpha 1 for the UPS3

if I understand it correctly, Alpha1 v UPS3
1. Alpha 1 is more energy efficient
2. Alpha 1 is noisier
3 Alpha 1 flow rate is much less

is this correct?
thanks
 
Does your version of the Alpha have the power displayed, watts, W?
Can you post a photo of the running pump with its LEDs displayed, this will show mode/setting.
How many rads?.

1&2 above, NO. 3. YES.,
 
Does your version of the Alpha have the power displayed, watts, W?
Can you post a photo of the running pump with its LEDs displayed, this will show mode/setting.
How many rads?.

1&2 above, NO. 3. YES.,
thanks for the reply, Yes it does have Watts Displayed &16 Rads, picture attached, say flow rate 2.4m3/h UPS3 say 4 on the Grundfos site, constant III setting
 

Attachments

  • alpha1.png
    alpha1.png
    379.3 KB · Views: 17
thanks for the reply, Yes it does have Watts Displayed &16 Rads, picture attached, say flow rate 2.4m3/h UPS3 say 4 on the Grundfos site, constant III setting
That pump is pumping absolutely nothing at 4W, setting 1 in PP mode.
16 rads, you will require ~ 1 to 1.5m3/hr at say a 3.5M head to service those 16 rads.
Suggest, as a start, setting it to CP2 (second symbol on the right) and setting 2, you will require ~ 25 to 30W, see what this gives you, if < 20W try setting 3, (CP mode)

Have you a link to your pump?.
 
That pump is pumping absolutely nothing at 4W, setting 1 in PP mode.
16 rads, you will require ~ 1 to 1.5m3/hr at say a 3.5M head to service those 16 rads.
Suggest, as a start, setting it to CP2 (second symbol on the right) and setting 2, you will require ~ 25 to 30W, see what this gives you, if < 20W try setting 3, (CP mode)

Have you a link to your pump?.
Sorry I think I haven't explained correctly, the picture is the brochure, my actual pump is running at 35watts in constant III mode

the brochure picture says flow rate is 2.4m3/h for alpha1 and according to Grundfos UPS3 says 4m3/h
 
Sorry I think I haven't explained correctly, the picture is the brochure, my actual pump is running at 35watts in constant III mode

the brochure picture says flow rate is 2.4m3/h for alpha1 and according to Grundfos UPS3 says 4m3/h
That's your pump curves below, I think.
Wht you have is three constant speed, CC settings, on the left, two PP modes first two symbols, on the right and two CP modes, last two symbols, on the right,

You are saying that you are running it on speed 3, III on the far left, is that correct??, if so at 35watts the pump is circulating ZERO, if you are saying the third LED on the right is illuminated then its running in CP1 mode and 35watts gives a flow of 1.6m3/hr, at a 3M head, is this it?.
To avoid any confusion can you just post a photo as requested.

1705779959391.png
 
Here you go picture of actual pump, thanks
Certainly looks as if running in full speed mode so it cant be circulating anything at 35W, the boiler (if a heat only) should only run for a few seconds/minutes and the rads will/should be completely cold IMO, its possible that the pump is full of sludge and choked, just change it to CP2 (far right symbol) and if it runs at ~ 5W then pump sludged up or a valve shut somewhere.
Only other explanation is that its a 35watt pump and not 45/50 watt.
 
Last edited:
The UPS3 is a far more powerful pump but won't consume any more power than the Alpha1 if running at the same head and flow. As its a bigger pump then it should run a bit quieter than the Alpha1 IMO
Cons, this model has a history of premature failures and disgracefully IMO, does not display the power.

If you don't mind, you might just change the Alpha1 mode briefly to CP2 and note the watts, then revert back, thanks.

1705784623782.png
 

Reply to Grundfos Alpha v UPS sorry cross post in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

I want to replace the three 11 year old Grundfos UPS 15-60 130 pumps as a part of trying to reduce the electricity consumption of my heating/DHW...
Replies
14
Views
6K
Jojomacjo
J
    • Like
Hello, my Mothers heating failed in the recent UK cold snap. I found the pump was stuck. I have a question about pump orientation. The...
Replies
8
Views
676
Hello forum, 1st time here. The Grundfos 3-speed pump in a Worcester Heatslave 15/19 oil combi boiler is on its way out. The boiler is old but...
Replies
4
Views
718
Hi everyone. Bit of a daft question but I’ve just had the pump replaced by the housing group where I live. They’ve fitted a Grundfos UPS3 15-50/65...
Replies
5
Views
1K
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
9
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock