Hi i wonder if anybody can help with my query, the only gas appliance i have is a ideal Mexico super cf455 boiler, historically my gas usage was 12kwatts a year it is now double that figure at around 24,000 kwh, the boiler is only on for very short amounts of time as in not left on all day/night, i have left it off for 24 hours and checked the meter, no gas was used. the boiler seems to be using 1.7 units which i calculate as 53 kwh in one hour of run time. i have spoken the the engineer who services the boiler and he said the unit would not burn double the the amount of gas and thinks it might be the gas meter, any help would be much appreciated. there is no gas cooking.
thanks
 
Where have you got your figures from?
The first is in Kw the second in Kwh. We need to clear up what you're saying first of all so we are all in the same units.

The 1.7 units:
Is that meters cubed? If it is then it doesn't add up to 54 Kwh.

If you can clarify those things, we can help more.
 
Where have you got your figures from?
The first is in Kw the second in Kwh. We need to clear up what you're saying first of all so we are all in the same units.

The 1.7 units:
Is that meters cubed? If it is then it doesn't add up to 54 Kwh.

If you can clarify those things, we can help more.
hi,
thanks for reply.
a 45 minutes example from day before
reading before on 4228.664 M3
reading after 4229.941 M3
gas boiler only on . no cooking.
thanks
 
hi,
thanks for reply.
a 45 minutes example from day before
reading before on 4228.664 M3
reading after 4229.941 M3
gas boiler only on . no cooking.
thanks
If we use that and calculate the Kwh, it is 19.298. That's using the correction factor/calorific value and so on that I use currently.

I thought you only had the one gas appliance?
 
hi,
thanks for reply.
a 45 minutes example from day before
reading before on 4228.664 M3
reading after 4229.941 M3
gas boiler only on . no cooking.
thanks
So you are using 1.28 m^3 in 45 minutes, which is 1.7m^3 per hour. That's about 19.3kWhr per hour.

If you have the boiler on at that rate for five hours a day for the four cold months of the year you'd use 11,740 kW hr.

This year has been a bit colder (in terms of degree days) than last year so your consumption may well be up by, say, 20% or so because of the weather this season.

Where did the '24,000 kwh' figure come from?
 
If we use that and calculate the Kwh, it is 19.298. That's using the correction factor/calorific value and so on that I use currently.

I thought you only had the one gas appliance?
sorry, yes only that gas appliance. Electric oven and hob.
does that usage sound alot for 45 mins for that boiler?

I had used following reading 4229.941 -4228.664 = 1.277 for 45 mins
or 1.7 units per hour
1.7 units x 2.8 x 1.02264 x39.1 /3.6 = 52.86 kwh
calcs from Octopus energy

thanks
 
So you are using 1.28 m^3 in 45 minutes, which is 1.7m^3 per hour. That's about 19.3kWhr per hour.

If you have the boiler on at that rate for five hours a day for the four cold months of the year you'd use 11,740 kW hr.

This year has been a bit colder (in terms of degree days) than last year so your consumption may well be up by, say, 20% or so because of the weather this season.

Where did the '24,000 kwh' figure come from?
 
sorry, yes only that gas appliance. Electric oven and hob.
does that usage sound alot for 45 mins for that boiler?

I had used following reading 4229.941 -4228.664 = 1.277 for 45 mins
or 1.7 units per hour
1.7 units x 2.8 x 1.02264 x39.1 /3.6 = 52.86 kwh
calcs from Octopus energy

thanks
I think that calculation is for an imperial meter, but you have a metric meter. it should come out at 19kWh ish according to an online calculator I used!
 

Reply to gas usage doubled to 24,000kwh in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

D
Recently noticed a gas smell coming from my ideal classic RS50 boiler. Cadent have been out and confirmed a small leak and capped off the gas. The...
Replies
1
Views
366
Had conventional boiler and tanks removed last year and new combi fitted and just recently had it serviced but the guy who did it has given me a...
Replies
9
Views
777
Hi all Wondering if you could help with this strange issue. I have a Vaillant ecotec 637 (set to 20kw part load) which was connected via a LLH...
Replies
57
Views
3K
Hi, moved into a home a year ago with what is probably an old heating system. There is a gas boiler linking to radiator central heating, and a...
Replies
4
Views
581
I have one of the attached heating coil unit (fan assisted) installed in my lounge. The Lounge is about 650sq.ft so instead of radiator we...
Replies
10
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock